Triangle Tube provides DHW, but no heat

Alan (California Radiant) Forbes
Member Posts: 4,426
We received two calls this week from homeowners, one that has a TT Solo and the other has a TT Excellence (combi). They have DHW, but no heat. I jumpered the thermostat connections at the boiler; nothing happens. Thumbing through their literature, I looked for a DHW only vs. DHW/heating setting, but found none. Also disconnected the outdoor sensor even though it was below 68F without any response from the boiler. Any ideas?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
-
See page 16 - Top right of page for "shortcut" that was probably activated by accident
https://triangletube.com/getmedia/773a8c23-9f26-4a7e-ba4a-37d210d98fca/PS-Control-Supplement-5-MCBA.pdf?ext=.pdf2 -
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Parameter 3 had a setting of "00", "Burner and CH Pump Disabled". Changed it to "01", "Burner and Pump Enabled" and the burner kicked on.
Ever since a power surge, the boiler was only heating DHW.
Thanks again, gentlemen!8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 975 Plumbing
- 6.3K Radiant Heating
- 386 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements