Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Pigtail
fxrgrunt
Member Posts: 157
Drained boiler today and in the process of cleaning inside, replacing sight glass and putting new pigtail. Does the new pigtail need to have water in the loop when installed or will that take care of itself?
0
Comments
-
It will eventually fill with condensation, but I like to put water in there to keep the controls from coming in contact with the steam (even if they might be fine).
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
There is no need to fill a pigtail. The first time the boiler runs the steam in the pigtail will condense and fill the pigtail making the required seal.
I have seen plenty of gauges and pressure controls installed for years with no pigtail and they survive.
But a pigtail should be installed. And the pigtail must be brass. Steel is a no-no2
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements