unimatch 24 volt feeder with 2 terminals.. not marked which is hot and which is neutral
Joseph_4
Member Posts: 296
Hi I am working on 2 boilers that both have an old unimatch 24 volt feeder for steam with only 2 terminals.. not marked which is hot and which is neutral. does anyone know which is hot and which is neutral or have wiring diagram?
Thanks
Joe
Thanks
Joe
0
Comments
-
You don't have a hot and neutral with 24V.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
If I am not mistaken, the older, 2 wire models, did not have a constant hot. One wire is neutral and one is hot only when there is a call for feed.0
-
Im trying to connect the new hydrolevel CG400 LWCO to the old feeder. quoting from instructions from hydrolevel (and Im asking for help cuz I dont want to short out either the feeder or the LWCO) " For water feeders with 2 leads, connect feeder neutral to terminal 2 and feeder hot to terminal A"
Thanks
Joe0 -
Is the old feeder still wired? You should be able to manually trace the wires backwards.0
-
one of them is... but runs into main power supply then goes into old Honeywell ring LWCO (not so familar with) and has second #67 LWCO so instead of breaking my head I was looking for an easier trip0
-
First, do yourself a favor and get a SafeGaurd, not a CycleGaurd.
Second, are you reading the instructions for a 24V model or the 120v model?
Again, there's no hot and neutral on the secondary side of a 24v transformer.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
See attached. I am assuming that H is for hot and N is for neutral.0
-
ok you were right....the wording went to hydrolevel site on 24v model says connect to "feeder common" and the "feeder hot" to terminal A... how do i know which is which?0
-
The MM 67 does not have a neutral. All wires running to the 67 are "hot". Not familiar with the Honeywell. Maybe you can post some pics.0
-
thats my problem those instructions have 3 terminals how can i make any assumption if control was changed0
-
here is pic
0 -
ok will be at tomm.. will let u know..0
-
H on the LWCO is the same as R on a 24V transformer andSTEAM DOCTOR said:See attached. I am assuming that H is for hot and N is for neutral.
N on the LWCO is the same as C on a 24V transformer
They have changed-up the designation to be able to use the C designation for Common on the NO and NC contacts in the LWCO. If you look at the internal wiring of the LWCO, C is common on the switch to B and W
To answer the OP question, Eliminate the wire from H to H on the LWCO to the feeder. Then it won't matter which wire is the B or the N. With only two wires you just need 24V alternating current (AC) since there is no additional circuit to deal with. You can reverse the wires and get the same result.
In the diagram for the Hydrolevel control, just eliminate the wire that I have colored pink.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Thank you so much Ed.. awesome!! Will implement today.
Joe0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements