If I'm thinking of the right messed up boiler, I think my answer is that the water is getting thrown into the mains by the bad piping, which makes it look like you are losing water during a heating cycle.
Did you observe the water level before the heat cycle, during the heat cycle, and after the heat cycle to see what the water level is like for each of those times?
If the level drops dramatically (more than a couple inches) during the heating cycle, but then recovers, the bad piping is almost certainly the cause. You will have to fix the piping, or you can try to keep it from happening with the current piping by ensuring your water is clean with not too high a ph, and try a water level on the low end of acceptable.
Adding water when it is low from this condition will just flood the boiler and give you even worse quality (wetter) steam.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I did observe the water level. The sight glass was full to the line indicating proper amount on Saturday. Sunday it was 3/4 down. Then last night it had only 1/4 in the glass, then later 1/2.
Thank you for your insights on this. I am more convinced than ever that bad piping is causing all of these problems. I don't want to see water continually added without resolving the underlying problems.
Unless it is leaking underground where one of the pipes does go (below cement) we do not see a leak.
Thanks.
1 -
Hi NBC - Attached is a photo of the boiler. You had asked in a previous post to see the auto feeder reset button (which I am no longer pushing because this needs to be resolved). I really appreciate any thoughts.
Thanks, too, Ethical Paul, for your help with this too.
0 -
OK thanks for that info. If the water level is truly going down that fast, then you have a leak. It might be in the boiler, or it might be in the buried returns.
Have you done the test that @nicholas bonham-carter mentioned above where you fill the boiler up to about ceiling level and leave it there for some hours (with the boiler shut down of course) to see if water pools under it? This is the test for a rusted out or otherwise leaky boiler.
If the water level drops but the boiler area is dry, that points to a leak in the buried return.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Show us where the pipe comes out of the ground and is connected to the boiler....back up for full picture.0
-
The plumber a year ago ran a test while the boiler was off to see if it was losing water and it didn't lose any. As far as the test that NBC recommended, I would need to ask a plumber to do that now to see something has changed.
Attached are some photos of the pipes going into the ground. The darker ones are the best I could do given there was no light in the boiler room and I backed up as far as I could
0 -
One more question - Does this pressuretrol and set up look ok to you?
0 -
-
Thanks. This is not good news for us but we will have to deal with it. We're interviewing new plumbers now and all this info you all provide helps me so much so we can make a good decision.0
-
First of all the boiler does not need to be dismantled to fix the piping.
What I would do with the boiler cold is mannually fill it ...over fill it until the supply piping coming off the boiler is cold. Let it sit for several hours over night is bette and look for leaks around the boiler. If you don't see any leaks on the floor or in the fire box after a few hours the boiler is probably ok
After that drain the boiler down to mid level in the sight glass and mark the level with a sharpie. Again let it sit overnight the level should not drop. If it drops you have a leak somewhere perhaps underground1 -
Ok, thanks, for this advice, Ed. Two plumbers have told us that they need to remove the entire boiler to re-pipe it properly. Thanks for your suggestion to check for a leak.0
-
I also like the suggestion that the boiler is forcing the steam too fast into the two mains and without a header, there is water being sent out that way and creating 'wet' steam. The pipes clang too much when the boiler fires up at times. It's all trial and error. We just hope we can avoid any more errors. Thanks everyone for your suggestions. I welcome any others you may think of along the way.0
-
-
steam2pipe said:Ok, thanks, for this advice, Ed. Two plumbers have told us that they need to remove the entire boiler to re-pipe it properly. Thanks for your suggestion to check for a leak.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
The folks telling you the boiler has to be removed to fix the piping probably don't have pipe threading machines and will just try and use copper for everything.
Near boiler piping carrying steam HAS TO BE THREADED BLACK STEEL PIPE and at a minimum it has to meet the manufacturers instructions. If I paid for a repipe i would want them to go over and above the manufacturers minimum requirements - an extra hundred dollars is nothing compared to the cost of repiping a boiler.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
Many manufacturers can supply a piping kit for the particular model of boiler, which will ensure the boiler is piped properly.—NBC0
-
Thanks so much. The contract to fix the piping says: "All items provided will be piped and sized to Weil McLain’s
Manufacturer specifications. The entire boiler will be stripped down back to the boiler only. All of the near boiler piping will be replaced." So maybe he is not 'removing' the boiler just stripping it down and I misunderstood. Does that sound right? The contract also says "black steel risers'. We were also just told today that copper piping is a mistake and that is the piping going from the boiler into the ground.1 -
Another thing to make sure of is: threaded risers, and header at least. Welded pipes will put an additional strain on the sections of the boiler.—NBC0
-
We were also just told today that copper piping is a mistake and that is the piping going from the boiler into the ground.
Copper pipe below the waterline is OKNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Yes copper below the boiler water line is not a problem0
-
Thanks, everyone. FYI -It is a proposal (not contract signed yet) that I quoted above. I don't see "threaded risers" just "black steel risers". There is a black steel header and black steel equalizing line with with Hartford Loop included. Good to know copper piping below water line is ok, too.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements