Bleeding HWB zones while boiler is hot
1075NH
Member Posts: 34
If this question has been asked and answered in another thread my apologies. I couldn't find it. My question is in regards to bleeding the air from zones on a residential cast iron Hot Water boiler. I have heard a lot of opinions on the "dangers" of bleeding zones while the boiler is hot. Namely cracking the boiler by introducing cold water. Especially when bleeding multiple zones for any length of time. Some people say let the boiler cool down to room temperature. In a perfect world, sure. But i have never heard of any boiler service tech going out on a call and saying they need to come back hours later when the boiler is at room temperature to bleed it. Is this an "Old wives tale"? Do i really need to leave the house with no heat or hot water for hours while i let the boiler cool before bleeding zones? Is it better the leave the boiler turned on while bleeding zones to heat the incoming water? I have asked a lot of plumbers and techs this question and the majority say it's fine. But a few insist you will cause cracks in the boiler that will fail sooner than later.
If you don't let it cool down to room temp what is a safe temp to allow bleeding zones?
Thoughts?
If you don't let it cool down to room temp what is a safe temp to allow bleeding zones?
Thoughts?
0
Comments
-
How much water are you bleeding out? And are you circulating at the same time? If it's only a gallon or two -- and I can't see it being more than that -- particularly if you are circulating at least the boiler, I can't see it being a problem. If you are taking a pretty dry system which is hot -- maybe shut down on low water or something evil like that -- yeah, that's a problem. Don't do it.
And I presume that the makeup water is going into the system piping, not directly into the boiler.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I'm talking about bleeding/purging air from the system using the standard procedure. So a hose connected at the purge station, return valves closed, PRV set to Fast Fill. So in some cases you are talking about flowing a lot of water for several minutes per zone. And the makeup water is feeding into the return side of the boiler (which is common).Jamie Hall said:How much water are you bleeding out? And are you circulating at the same time? If it's only a gallon or two -- and I can't see it being more than that -- particularly if you are circulating at least the boiler, I can't see it being a problem. If you are taking a pretty dry system which is hot -- maybe shut down on low water or something evil like that -- yeah, that's a problem. Don't do it.
And I presume that the makeup water is going into the system piping, not directly into the boiler.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements