crawl spaces

scrantch
scrantch Member Posts: 38
Is piping in a crawl treated the same as if it was under a slab? Or can there be connections for gas or water?

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    scrantch said:

    Is piping in a crawl treated the same as if it was under a slab? Or can there be connections for gas or water?

    What? Little more detail, please.

    There was an error rendering this rich post.

  • scrantch
    scrantch Member Posts: 38
    What type of pipe should be used for propane when the runs are in a crawl space
  • Intplm.
    Intplm. Member Posts: 2,155
    To my knowledge there are no restrictions for workmanship from a basement to a crawl space of any kind.

    Of course, all local / mechanical codes should always be followed. So, check with your local code official.

    Material requirements are most likely the same in a crawl space to basement etc.

    What type of material are you considering?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,283
    What @Intplm. said
  • scrantch
    scrantch Member Posts: 38
    I was going to use 3/4 " black pipe hung from the floor joists but thought because it was a crawl instead of a basement they might require no threaded connections until it exited the space
  • HVACNUT
    HVACNUT Member Posts: 6,239
    edited October 2020
    scrantch said:
    What type of pipe should be used for propane when the runs are in a crawl space
    If the crawl is not air sealed then use galvanized pipe. Black will rust. You can use fittings. 
  • scrantch
    scrantch Member Posts: 38
    HVACNUT said:


    scrantch said:

    What type of pipe should be used for propane when the runs are in a crawl space

    If the crawl is not air sealed then use galvanized pipe. Black will rust. You can use fittings. 

    Thanks, it is sealed pretty good with plastic membrane on the slab and foam sprayed up the walls to the deck. There must have been moisture issues.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,283
    @scrantch

    Depends where your located. Some states do not allow galvanized pipe for gas.

    Massachusetts is one.
  • ChrisJ
    ChrisJ Member Posts: 16,235
    I used all black iron in my crawl spaces and there's really no surface rust on any of it, at least not yet in 10 years.

    To be fair, there's plenty of slightly rusted fittings out there in basements. How long do you think it'll take to rust through a fitting in a damp basement or crawl space?

    From what I've seen, many areas don't even enforce painting / protecting black iron gas pipes outdoors. They just let them rust.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • motoguy128
    motoguy128 Member Posts: 393
    We have tons of really wet basements with 50-100 year old black pipe.  really no issues.  

    I would avoid using any unions down there. Some local code May forbid it.   Mostly because of access issues.  

    Our company would run a CSST product like TracPipe as it’s easier to run and hang in tight spaces and you can turn corners.   Have to use appropriate flanges and fittings to pass through floors and walls per mfg spec and code.  

    But honestly I still prefer dragging the threader  to the job site and doing it right.  

    Soap all joints and perform shut in test.  
  • ChrisJ
    ChrisJ Member Posts: 16,235

    We have tons of really wet basements with 50-100 year old black pipe.  really no issues.  


    I would avoid using any unions down there. Some local code May forbid it.   Mostly because of access issues.  

    Our company would run a CSST product like TracPipe as it’s easier to run and hang in tight spaces and you can turn corners.   Have to use appropriate flanges and fittings to pass through floors and walls per mfg spec and code.  

    But honestly I still prefer dragging the threader  to the job site and doing it right.  

    Soap all joints and perform shut in test.  
    Shut in test?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Depending on the load served, soft copper may work out well. I've run many many feet of copper for propane. If natural gas is ever a possibility, then black pipe. I would avoid CSST personally. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    SuperTech
  • mattmia2
    mattmia2 Member Posts: 10,755
    Pretty sure code will require a pressure test unless it is a small modification.
  • mattmia2
    mattmia2 Member Posts: 10,755
    Why is copper allowed in some places for methane and not in others?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,283
    @mattmia2

    In my area copper is ok for propane, but not natural gas
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    I was always under the impression that the same Mercaptain operant was used in both NG and LPG. 

    I thought it was trace amounts of sulfur that were once found in NG that was not compatible with copper. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    Larry Weingartenmattmia2kcopp
  • mattmia2
    mattmia2 Member Posts: 10,755
    I think the model code says something like you can use copper if it has under some sulfur content but I don't know what that means in practice since I don't think you have control over the source of the gas over the many decades that it will be in service.
  • ChrisJ
    ChrisJ Member Posts: 16,235
    I'm just over here wondering what a shut in test is...............
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    Solid_Fuel_ManAlan (California Radiant) Forbes
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,563
    Hi @ChrisJ , Maybe it's a Texas thing: "A gas shut-in test, if ordered, is performed at the time of inspection. It tests to see if there are any natural gas leaks in the home and between the home and the meter. This is not included in the structural/mechanical inspection.
    Gas Shut-In Test - Texas Panhandle
    panhandleinspection.com/gas_shut-in_test.htm "

    Or, perhaps it's the new test we're all doing, more or less while living through the corona virus o:)

    Yours, Larry
    Alan (California Radiant) Forbes
  • ratio
    ratio Member Posts: 3,774
    That must be where they close all the doors & windows, & wait to see if the inspector smells gas. :wink::wink::wink:
    Solid_Fuel_Man
  • TAG
    TAG Member Posts: 757
    Just went through this ... the "rules" are all over the place. Plumber says one thing ... town another. Propane company another. Then it all changes depending on who comes out.

    The flex SS with cover is allowed almost everywhere inside -- I did not want it used in some areas that I will not be able to get to after construction .... like a spray foam insulated floor over an insulated slab. Across a ceiling in the kitchen. They used black pipe. Flex in the crawl space, basement. No copper -- only allowed on exposed small systems with above ground tank.

    I even had issues with the main line from the tank --- propane company said to run 2" water line in trench to the house for future propane fish when doing all the services. The project was delayed and they sent a guy who said "not allowed" ... had to get propane company rep and inspector out to look at it. Both looked at it and said that was the way they always did it years back when any rocks around?
  • ChrisJ
    ChrisJ Member Posts: 16,235
    TAG said:

    Just went through this ... the "rules" are all over the place. Plumber says one thing ... town another. Propane company another. Then it all changes depending on who comes out.

    The flex SS with cover is allowed almost everywhere inside -- I did not want it used in some areas that I will not be able to get to after construction .... like a spray foam insulated floor over an insulated slab. Across a ceiling in the kitchen. They used black pipe. Flex in the crawl space, basement. No copper -- only allowed on exposed small systems with above ground tank.

    I even had issues with the main line from the tank --- propane company said to run 2" water line in trench to the house for future propane fish when doing all the services. The project was delayed and they sent a guy who said "not allowed" ... had to get propane company rep and inspector out to look at it. Both looked at it and said that was the way they always did it years back when any rocks around?

    My dad had the same issues with running a conduit for the propane line.

    Some said it wasn't allowed, propane company said it's fine.

    I wish we had some kind of rule book to go by so everyone would agree.................
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ratio
    ratio Member Posts: 3,774
    That's the beauty of standards. There are so many to choose from!
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    The whole thing with a conduit (raceway) for propane or NG for that matter, is the danger of a leak following the conduit into the structure. I always seal the end into the structure, and leave the outdoor end (usually at the tank) open and the inspector is happy. Well now water will fill it up and freeze.....

    Seems we would seal both ends, if there is a leak well....if it were direct burial it will still find it's way into the building. 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    mattmia2
  • ChrisJ
    ChrisJ Member Posts: 16,235
    The whole thing with a conduit (raceway) for propane or NG for that matter, is the danger of a leak following the conduit into the structure. I always seal the end into the structure, and leave the outdoor end (usually at the tank) open and the inspector is happy. Well now water will fill it up and freeze.....

    Seems we would seal both ends, if there is a leak well....if it were direct burial it will still find it's way into the building. 
    In my dad's case the conduit stops a foot from the building where the tubing comes out and goes up to the regulator outside.  Then that is plumbed into the house up at the sill.

    You have to dig down to the ends of the conduit to access it at both sides but it's far better than digging the entire length.   He originally did it because they were driving heavy machinery over that area to build the house and he didn't want issues with the freshly buried tubing.  But it came in handy recently when they ran a second line to feed a generator.


    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • mattmia2
    mattmia2 Member Posts: 10,755
    This appears to describe the pressure test required in the fuel gas code:
    https://www.amarillo.gov/home/showdocument?id=20130
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,283
    @Solid_Fuel_Man

    is right about a gas leak following a pipe or conduit. That is the reason most all gas meters are installed outdoors now rather than in the building. Same with propane usually go from the tank underground and up on the outside of the building to the reg