Radiant
kporter
kporter Member, Email Confirmation Posts: 2
edited October 2020 in Radiant Heating
Why would my circulator pumps on my Wirsbo 311 be running when system is not calling for heat? Warm weather shutdown down is active but floor is getting warm
  • Zman
    Zman Member Posts: 7,614
    Do you have an indirect water heater? Are there check valves installed?
    I picture with description of which circulators are running would help.
    Albert Einstein
  • kporter
    Have variable speed injection pumps on a completely Wirsbo system 17 years old. Pumps have internal checks. Pump running is the loop circ.
    hot_rod Member Posts: 27,703
    there must be a t stat calling, a shorted wire, or a stuck relay.
    Has it worked in the past?
  • Big Ed_4
    Big Ed_4 Member Posts: 3,545
    Is there a floor sensor on radiant job ?
  • Zman
    What is the controller telling you? Does it have a target temp and a percentage of modulation?
    I would verify that all the sensors are being read by the controller and are attached to the pipe. The controller will do weird things if input data is bad.
    BTW, that is a rebranded Tekmar, if you are having trouble finding manuals you can usually match it up with a Tekmar.
    Albert Einstein