Slow drip from taco pressure reducing valve

occicat
occicat Member Posts: 4
Hi all,
I've got a forced hot water system powered by a weil mclain lp hot water heater and the Taco pressure reducing valve has started dripping slowly. It's more pronounced now that the heat is actually getting used.

The boiler pressure kPa is reading just under 30 ( I am not sure if this is normal I'm suspecting it isn't as the valve is either failing or trying to keep up with pressure reduction and is dripping )

Another thought would be the expansion tank possibly failing causing more pressure?

What could be some steps I could take to either troubleshoot or is this a clear cut case of shut the water off before the Taco reducing valve and install a new one?

Pics below to illustrate further.




Comments

  • TomS
    TomS Member Posts: 66
    Your pressure gauge is actually reading about 30 PSI or about 200 KPa. This is too high. The gauge should read about 12PSI.
  • psb75
    psb75 Member Posts: 906
    Why are there TWO pressure reducers in-line. Older and newer?
  • neilc
    neilc Member Posts: 2,854
    can we see another picture showing the entire boiler and all the pictured parts above
    known to beat dead horses
  • neilc
    neilc Member Posts: 2,854
    and I think the second "reducer" is actually a backflow device,
    it says drain on its bottom open port,
    that where you're seeing the drip? or from the safety valve?(not pictured)
    known to beat dead horses
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378
    Replace the No. 30 Extrol

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    SuperTech
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378
    edited October 2020
    OK, That is a combination pressure relief valve, pressure reducing (auto feed) valve sold as a package. (this is today's version )
    https://www.supplyhouse.com/Taco-334-T3-Taco-Dual-Unit-Valve-Threaded-1995000-p?gclid=Cj0KCQjwxNT8BRD9ARIsAJ8S5xaY9A2RJvL4X6tmvYP35BvryqS8CxVpJ4iPd-aNbUIfDi3Dk5q4FaEaAh51EALw_wcB
    The relief valve portion is designed to release pressure at 30 PSI. So it appears that the relief valve is don't its job. that is letting excess pressure at 30#. The longer you have the relief valve opening to release water pressure, the more likely it will fail permanently and not close when the pressure is reduced below the 30# setting.

    When water is heated, it expands. When water cools off. it contracts. Consider you have a full system with no air in the radiators and no air in the boiler... Where does the expanded water go when the burner comes on and heats the water. Remember it is a closed system with no openings anywhere. Think of it like a bottle with pipes attached... all filled with water and no other openings anywhere.
    Water can't compress so Hydraulic pressure builds up as the water is heated and BOOM... or if you have a relief valve...Then... Swoosh or drip, drip, drip.

    If you have a tank filled with air, (Air can compress) then the expanded water can go into that tank and compress the air. When the water cools off and gets smaller, the compressed air can push the water from the tank back into the boiler and radiators because it is now less water.

    My guess is the Extrol No. 30 tank has no air left in it. That tank is designed to have 12 PSI air pressure in it from the factory. The air is separated from the waterside by a membrane called a bladder. If the blader is not compromised you can add air to the tank. If the bladder is compromised then the tank needs to be replaced. By the look of it, the tank is pretty old and the bladder is most likely compromised.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378
    psb75 said:

    Why are there TWO pressure reducers in-line. Older and newer?

    They are not the same item, look closely, and see one has a drain hole in the bottom, the other does not. the drain hole is leaking because the boiler is at 30 PSI. the relief valve is supposed to let water out at 30 PSI. My guess is... that part is working properly.

    There should be a safety tube attached to the relief valve that extends to a drain or at least to within 6" of the floor

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • neilc
    neilc Member Posts: 2,854
    what I was getting at with the request for boiler picture is -
    is there a domestic system attached to the boiler also ?
    known to beat dead horses
  • JUGHNE
    JUGHNE Member Posts: 11,274
    There may be another pressure relief valve on the boiler also.
    What is the cold pressure of the boiler?
  • psb75
    psb75 Member Posts: 906
    To EdTheHeaterMan: So...what IS that other item in the picture with the identical green "bell" cover with a pressure reducing stem on top? It seems to have a threaded hole on the bottom too, with a hex plug in it. Odd that.
  • neilc
    neilc Member Posts: 2,854
    the one on the left is the "primary" reducer,
    there's (was) a screen inside that bottom,
    known to beat dead horses
  • psb75
    psb75 Member Posts: 906
    I don't understand a "primary" reducer. So the other is a "secondary "reducer? I need to know if this is an hydronics principle with which I am not familiar.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378
    edited October 2020
    @psb75
    look at this: https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Pressure_Reducing_Valves329-329T-335-334-334TInstall2222.pdf
    it is the most current version.

    The one on the left is the pressure-reducing valve, the one on the right is a standard 30 PSI relief valve. Many boilers before 1930 did not come with relief valves. This was an easy way to include a relief valve with the installation.

    When these feed valves are left in place during a modern boiler install. (1960 to present) the new boiler has 2 relief valves. The one that comes with the boiler and the one left behind by the installer of the new boiler

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378
    psb75 said:

    I don't understand a "primary" reducer. So the other is a "secondary "reducer? I need to know if this is an hydronics principle with which I am not familiar.

    I don't understand this either.

    I'd like a further explanation from @neilc
    Does the fact that there is a primary mean that there is a secondary pressure reducer?

    I think not, but correct me if I'm wrong.




    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • psb75
    psb75 Member Posts: 906
    Thanks Ed. I've never seen this assembly before. The one on the left is a pressure only, relief valve. Not temperature. And the one on the right is the pressure setting valve with a quick fill lever. Seems like it lets a lot of water in, especially for purging.
    EdTheHeaterMan
  • neilc
    neilc Member Posts: 2,854
    let me try this again,
    and look, I'm no expert, I just play one on the internet,

    the one on the left is a pressure reducing regulator, it has the adjustment screw up its top, and a filter screen inside that bottom cap.

    the one on the right, with the drain port on its bottom, is or ought be a backflow protection device,
    and I don't see any fast fill lever on its top, for that matter, how would a fast fill operate AFTER the pressure reducer?
    wouldn't it need to be one assembly, like a modern pressure reducer w/fast fill ?
    looking back at the picture one more time, if that is a lever up there, I'm gonna call it a test lever to check the valve, the safety valve, and I'm no longer calling it a backflow.

    I'll be over here.
    known to beat dead horses
  • neilc
    neilc Member Posts: 2,854
    and now looking at Ed's link,
    I'll stand down
    known to beat dead horses
  • JohnNY
    JohnNY Member Posts: 3,291
    TomS said:

    Your pressure gauge is actually reading about 30 PSI or about 200 KPa. This is too high. The gauge should read about 12PSI.

    The pressure reading on the gauge, whether static or dynamic, is based on the height of the system. I see nothing in the post referring to elevation.
    neilc said:

    I'm no expert, I just play one on the internet,

    the one on the right, with the drain port on its bottom, is or ought be a backflow protection device,

    @EdTheHeaterMan deserves a big thank you for his input in this thread that is otherwise full of a lot of highly confident guesswork.

    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    EdTheHeaterMan
  • neilc
    neilc Member Posts: 2,854
    thankyou Ed
    known to beat dead horses
    EdTheHeaterMan
  • neilc
    neilc Member Posts: 2,854
    edited October 2020
    how many "atta boys" to make up for the "ah sh1t" ?
    known to beat dead horses
    SuperTechEdTheHeaterMan
  • occicat
    occicat Member Posts: 4
    neilc said:

    can we see another picture showing the entire boiler and all the pictured parts above

    Certainly, here is another photo of the entire unit and another of the reducing valves.

    This would be in the NH area, so elevation would be related to my geographical location which hopefully helps.


    a
  • occicat
    occicat Member Posts: 4

    So I finally got around to swapping out the old expansion tank with a brand new one. Checked that it was charged at 12 psi, and replaced the tank. Upon installation I checked the tank again and it reads 16psi.


    The gauge on the boiler still reads a tad below 30 and the pressure reducer valve still drips.


    I am at a bit of a loss as to what the boiler pressure reading should actually be, since I don’t have any baseline for what is normal, perhaps 30 psi is normal?


    I also asked my local municipality about any change in water pressure and was told it’s all gravity based and they couldn’t offer any assistance.


    My only other thought is that there is air in the system still causing a rise in pressure, not sure what else to do other than order another pressure reducer valve and hope that sorts it but from reading Ed’s explanation, I don’t think that’s the case.


    One other thought is that the main water line splits, one going through the pressure reducing valve to the boiler and another that bypasses the valve and goes to a hot water boiler with its own expansion tank.


    That tank on the hot water boiler side reads at 51psi and it’s made by Watts. I did not install this so it’s unknown if it was set to 12 psi as well or not. It is a few years old and not leaking. 


    My thought is that perhaps that pressure is too much and backfeeding into the line causing the higher boiler pressure? Or perhaps the taco reducer needs to be reduced to 12psi and not 30?


  • Jamie Hall
    Jamie Hall Member Posts: 24,848
    Hopefully the domestic hot water heater (boiler?) has no connection to the heating boiler, other than the feed lines. It should have an expansion tank (and you mention one) and its pressure will be that of the domestic water supply. 51 pounds sounds about right.

    Unless you have an exceptionally tall house, however, the pressure in the heating side when the system is cold should be between 12 and 15 psi -- no more than that. Ideally the pressure gauge on the heating boiler should show that pressure, but unhappily they have been known to lie. As a first pass, though, try closing the valve in the water supply from your domestic water and draining some water from the heating system -- not much, mind you -- and that gauge should show a drop in pressure. If it does, try draining a bit at a time so that it reads 12 to 15 pai. Now the fun part: reopen the valve from the water supply. The pressure should stay about the same. If it doesn't -- if it rises -- the pressure reducing valve is either shot or not correctly adjusted. If the installed pressure gauge doesn't cooperate, you can get a gauge from the big box and a few fittings and connect it to a handy drain and use that.

    And kindly report back...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • occicat
    occicat Member Posts: 4
    I had just replaced the leaking gaskets on the circulator pump and the gauge did indeed go down to zero then back up again when everything was put back together.

    I did try what you suggested above and it made no difference. I then adjusted the pressure reducing valve and that made no difference.

    So, I put an order in for a replacement and some new shutoff valves and will swap this out and hopefully then, the leaking will cease and the boiler will read around 12psi.