Tar Paper + Concrete + Radiant Heating
pyrogerbil87
pyrogerbil87 Member Posts: 1
edited October 2020 in Radiant Heating
I am planning to install radiant heating in the 2nd floor of my home and was concerned about the smell from tar paper. My floor will consist of wood planks, tar paper, pex piping, self-leveling concrete, and wood flooring. My concern is whether the tar paper smell in either the upper floor or lower floor when the radiant heating is on.
  • STEVEusaPA
    Not a problem, although I’m concerned about the sandwich of gypcrete then hardwood over it.
  • GroundUp
    GroundUp Member Posts: 2,527
    I wouldn't think it'd smell, but I am wondering why you'd put tar paper over your planks at all. To keep the gyp from dripping through? How thick will the gyp be?
  • Paul Pollets
    Paul Pollets Member Posts: 3,672
    Red rosin paper should be used, not tar paper. The only hardwoods that should be used for direct placement on the slab would be pre-engineered hardwoods, rated for the application. Strip oak flooring can be applied if 2 sheets of plywood are placed on the floor prior to installing the strip oak. (Bollinger method) That method is rarely used anymore due to the cost of the plywood and the additional height of the finished floor.
    Zmanmrhemi
  • TAG
    TAG Member Posts: 806
    Why the concrete ? are the floors way off?
    I have done about 10 projects (personal) -- pushing 30 years -- all of them have radiant under wood floors. Including some with very wide planks -- 10+ inches.
    They all had heat loads done and did not have 150 degree water running through them.
  • Zman
    Zman Member Posts: 7,614
    @pyrogerbil87
    It sounds like this might be an older home. Has anyone evaluated this structurally? I would be concerned with both the additional dead load and the deflection.
    Albert Einstein
    hot_rod Member Posts: 27,817
    edited October 2020
    probably what you have is asphalt impregnated felt paper :)
    It can handle the temperatures that you would typically run in gyp pours. Most of the engineered hardwood can be floated over gyp, tile sheet products like linoleum.
    You need to run the system for days to dry it out, lots of water in gyp pours and it comes out the top.
    A sealer can be put on also. I have seen tile over gyp, but you really don't want to get it wet. Even sealed it tends to come apart when wet, not unlike sheetrock.
  • fuzzyjohn
    fuzzyjohn Member Posts: 1
    Did you ever figure this out? I’m looking for the same answer.
    mattmia2 Member Posts: 17,459
    I think everyone suggested wood and aluminum transfer plates of some sort would be the way to go.