Pipe sizing for radiators
mow
Member Posts: 12
I'm removing fin and tube and replacing it with cast iron radiators. There are 4 radiators totaling 30,000 BTUs at 170°
I would be piping it with a separate supply and return.
Is 3/4 copper big enough to supply these radiators?
I would be piping it with a separate supply and return.
Is 3/4 copper big enough to supply these radiators?
0
Comments
-
You need to determine the output of each radiator and then use the sum to determine the main lines.
A 1/2" line can carry 1.5 gpm or 15k btus at std. 20* delta T.
A 3/4" line can carry 4 gpm or 40k btus " " " " " " " " " .
A 1" line can carry 8 gpm or 80k btus " " " " " " " " " ".
This is at 4 fps which is the maximum recommended velocity.
Don't mix piping methods or sizing on the same zone since water will take the path of least resistance. In other words, if you have over-sized piping (like that from an old gravity system), don't put that on the same pump as this new piping.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I have a similar question. Replacing fin-tubes for Runtals in bedrooms and baths that are at the far end of the house away from the boiler. To avoid running 10 ea 1/2" lines, I plan to run a pair of larger (secondary) pipe to a manifold on that end of the house, then run the 1/2" to the 5 radiators (approx 23K BTUs. How should I size the large supply/return lines between the near boiler piping and the manifold?0
-
The 5 half-inch ports on each 1" manifold body should be fed with 1" pipe. 5 x 1.5gpm = 7.5gpm.
1" pipe can carry 8 gpm.0 -
Unless I'm missing something, I don't see why they'd need 1 inch pipes to a manifold that is supplying a zone with a 23k btu heat loss. 3/4 inch should be more than enoughYou can have it good, fast or cheap. Pick two0
-
It depends on what the delta t is on your emitters, right?0
-
Thanks gents! You confirmed my lower math calculations at 20 delta T, I plan to run a new 1" straight run of copper to a 1" manifold. I tore out all of the old steel pipe. Two 3/4" loops out to the front and rear perimeter, then back through an old 1.25" steel down the center of the house back to the boiler room. It was full of black sludge. Thanks again!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements