gas-fired water boiler does not start;
sba
Member Posts: 7
Hi, my gas-fired water boiler does not start; the pilot is fine, so gas is there, thermal fuse is fine. Pilot is automatic (i.e. not permanent & starts only when needed) so control is fine. It seems the gas does not flow thought the main pipe but I do not know why.
Pilot goes on for 15s then goes off.
i would need help to figure out what the issue is.
Pilot goes on for 15s then goes off.
i would need help to figure out what the issue is.
0
Comments
-
Cleaning flame sensor often fixes this.....easy and free.
If a rod or part of the spark ignitor easy to clean with steel wool.
If a combined hot surface ignitor combined with sensor function, not real cleanable.....fragile.
It may glow but not sense flame as needed to keep gas on.0 -
More info is needed, like make and model of boiler, gas components, etc.
If you don’t have the tools and training to work on gas, you’ll be safer having someone who does look at it.
Try the contractor locator above.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
thanks for your help.
it is a weil mclain 1135-605. Natural gas i guess0 -
Can you post a couple of pictures of the boiler and controls?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
-
It would appear to be the flame sensor. Can you show a video of the pilot flame making contact with the sensor?
Thanks0 -
I ll make a video when I ll be back home.
Actually there no flame beside the pilot.0 -
here is the video - https://photos.app.goo.gl/toZSEDAfrjQUP4bB9
not easy to see the sensor since it is behind the pilot.
I can remove the cover of the boiler to get a better video.
thanks again for your help0 -
The pilot flame looks probably good enough.
Does the spark igniter have both of its "legs" in the flame?0 -
yes; the "legs" are in the flame0
-
A volt meter and manometer would be awesome about now.0
-
If you remove the flame roll out shield with the hole in it for pilot viewing you may reach the spark ignitor and carefully clean with a SS wire brush or a strip of sandpaper....I use a soft minor abrasive flexible sanding pad cut into strips.
Still shot picture first that we could see.
You need to clean both legs of this. Especially where the flame lands on the legs.
Do not change the spark gap or bend either of the legs.
Replace the shield and try again.
Let us know.0 -
I have cleaned it up; here is the video after (without the shield) there is a picture as well
https://photos.app.goo.gl/Npm8aNYKyMJZ8XPd8
0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements