Heat zone question.
Options
Redduc97
Posts: 15
I'm designing a new heating system(not a professional) and I have a 400 s.f. family room with about 24' of baseboard heat. Could I add a new basement room to this to help with short cycling? Both rooms would be on one zone controlled by a t-stat in the family room.
0
Comments
-
If you have separate zone pumps, you could also arrange a thermostatically controlled mixing valve to bring some of the return from that baseboard back into the feed to the baseboard, and run the baseboard at a constant temperature all the time... look up primary/secondary piping!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
It's all about the boiler output matched to the heat emitter. What type and size of boiler? If it is a non modulating cast iron for example, that would be a very small load and would lend itself to short cycling. 24' of fin tube might be around a 12- 15,000 BTU/hr load., figure around 550 btu/ ft of finned tube as a starting point.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I was looking at a Burnham K2 boiler (80,000 BTU) with a min. fire rate of 8000 BTU. I thought the 24' of fin tube would not keep the boiler from short cycling. I'm planning on finishing the basement room directly below this room and thought I could just add some more fin tube to the zone. The house is in Massachusetts.0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements