Tstat and vent damper wiring

Precaud
Precaud Member Posts: 370
edited October 2020 in Strictly Steam
I'm about to install a GVD-6 vent damper and new thermostat in my steam system, and thought I should get some input about how best to hook then up. The old tstat only had battery power, while this one (Honeywell TH5110D) can use either batteries or the 24VAC. Here's a diagram of how things are wired now.



As you guys probably know, with AC coming out of a transformer, there is no defined "Ground" or "Common", it can be either side. So how it's wired probably decides which is which.

1. My guess is, the red wire out of the xfmr is the most likely "common", yes?
2. So, if I want to avoid using batteries to power the tstat, then the red wire gets connected to the C terminal (common) on the tstat, yes? (This is pretty obviously so but I'll ask it anyway)
3. What's the best way to hook the vent damper relay into the system? Insert it anywhere in the series daisy chain? Or outside the loop?

TIA for your input.
1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,251
    I would think red would be hot but it probably doesn't matter. Based on the colors and polarity above yes C on the stat would be the red wire.

    Does the vent damper have a proving switch? Two wires to drive the damper and two wires to interlock the burner circuit?
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,135
    edited October 2020
    So to start with Electric is colorblind.
    We assign colors to help us determine what wire is at the other end of a long run of wire.

    We (the Pros in the industry) like to see a C on the transformer as common and an R on a transformer as the starting point of the power The starting point on your diagram is labeled "WHT" and goes directly to the thermostat "YEL". The important question at the thermostat is the terminal designation on the thermostat.

    Is "YEL" connected to the terminal designated as W or R on the thermostat? This is more important than you might think.

    If your transformer does not have C and R terminals then it has colored wires. (if the wire has a stripe in it, that is Common) and R is the starting point or "POWER". A complete circuit goes from POWER to a LOAD and back to the source at COMMON.

    The next point is that we prefer all the Safety and Limiting devices are in series before the device that operates the main burner (or gas valve).

    There is a reason for this that I remember learning about years ago, I just forget what the reason was at this time (AGE DOES THAT YOU KNOW) .

    So your diagram is somewhat flawed, but that does not mean it is not safe or that it won't work. It just means that adding the damper will be more difficult to figure out.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • JUGHNE
    JUGHNE Member Posts: 11,248
    Can you easily change the cable to the t-stat?
  • Precaud
    Precaud Member Posts: 370
    edited October 2020
    @EBEBRATT-Ed Yeah, the convention is Red = Hot, but we can just take the colors as identifiers it this case. Yes, the damper will have two wires to power it, a 3rd for the call-for-heat, and the fourth the proving switch.

    @EdTheHeaterMan , yes yellow is connected to R on the tstat, and black is to W.

    I know the existing wiring scheme works - it has worked for decades with two different tstats. But if there's a better or safer ordering, pls tell. Rewiring is not a big deal.

    If I understand you correctly, you would swap the LWCO and gas valve positions in the diagram, yes? Or just get the gas valve at the bottom of the tree?
    1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
  • Precaud
    Precaud Member Posts: 370
    JUGHNE said:

    Can you easily change the cable to the t-stat?

    ? Por qua ?
    1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,135
    edited October 2020
    Try this
    The labels on your gas valve are reversed. see the Red from the Damber should go the TH or R on the gas valve and the Wht on your gas valve should be TR or Common

    I have moved the thermostat to the R side of the transformer and connected transformer R to thermostat R.

    It makes more sense for someone unfamiliar to better understand later (years from now).

    Thermostat W now feed power thru all the limits and safety devices to power up the damper (check your damper wiring to see if it conforms to the diagram)

    Bl or Blue wire to the damper gets a 24V signal in order to open. The Bk or Black wire is powered with 24 V all the time.

    The W or White wire is common for the damper to have a return circuit to close the damper after power from Bl is turned off by thermostat or limit.

    The R or Red wire is connected to the safety switch in the damper so the burner won't operate unless the damper is fully open.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Precaud
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,135
    IMPORTANT Note that the Molex plug changes colors from one side to the other.

    If you decide to wire the system without the Molex plug please adjust the wire colors accordingly.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Precaud
    Precaud Member Posts: 370
    edited October 2020
    Thanks much, @EdTheHeaterMan . Great cut-and-paste job, BTW! I haven't received the damper yet, it is due to arrive Monday. But I think I can change the wiring to what you suggest relatively painlessly; all connections are easily acccessible. I'll be making my own harness for the damper, so whatever the color scheme ends up as, I will definitely be leaving a wiring diagram for a future owner to refer to.

    1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,135
    if it comes with both ends of the Molex plug, I would use them to make repair/replacement easy. If it does not. then double check the wiring instructions that come with the damper. If it is a replacement part for some other boiler, it may not have both ends.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Precaud
    Precaud Member Posts: 370
    It's a standard GVD-6 from Field w/o harness, I don't think they supply a plug with it. But we'll see shortly. It is no doubt a standard Molex plug that I can order from Digikey or similar. I already have a good selection of their connector inserts and crimping tool.
    1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
  • motoguy128
    motoguy128 Member Posts: 393
    Another option is to take the opportunity to upgrade the boiler to spark ignition and use a standard Honeywell Control that already has the plug on the board. Or upgrade your controller and keep the other as an emergency spare if it’s already DSI But older controller. The damper can be powered open and parked if needed. NEVER open the damper manually.

    Depending on flame sense setup... but here’s a few

    https://www.supplyhouse.com/ICM-Controls-ICM290A-Universal-Intermittent-Pilot-Gas-Ignition-Control

    https://www.supplyhouse.com/Honeywell-S8610U3009-Intermittent-Pilot-Control-4584000-p

    And the full kit
    https://www.supplyhouse.com/Honeywell-Y8610U4001-Intermittent-Pilot-Control-Conversion-Kit
  • Precaud
    Precaud Member Posts: 370
    For those who prefer to make their own wiring harness to a GVD damper, the connector for the cable end is a Molex 150179-2040, available at Digikey or Mouser for 43 cents ea.
    https://www.mouser.com/ProductDetail/Molex/150179-2040?qs=/ha2pyFaduhf66pxh2jZEZt12ojzqnleL8NHbpwBl2nfcph1hY56Yw==

    You'll also need four of the 150181-1016 female pin connectors at 10 cents each:
    https://www.mouser.com/ProductDetail/Molex/150181-1016?qs=OAhjpuo3Vu730aRyQweZFg==
    1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
    ethicalpaul
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,135
    edited October 2020

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    ethicalpaul
  • Precaud
    Precaud Member Posts: 370
    There is no connector on the boiler end of my ol' Bryant...
    1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
    ethicalpaul
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,135
    edited October 2020
    there must be a boiler end. You certainly can't put both ends of the wire on the damper???

    Should I call it the "heater end" or the "system end" whatever end you want to call it. (let's just call it the other end) The standard extension cord that connects the damper to the heater has a 4 pin on one side (Damper side) and a 6 pin on the other end. This is evident in the diagram that comes with the damper instructions... That is why I mentioned that electric is colorblind and you should adapt wire colors from my diagram to your system accordingly.

    It is now obvious to me that the connecting cord did not come with the damper. This will make connecting the wiring somewhat difficult. Probably should have ordered the connecting cord with the damper. Getting the 4 pin connector is a good idea.

    here is one already made
    https://www.supplyhouse.com/Hydrolevel-45-353-Wire-Harness-for-Connecting-Safgard-1100-and-1100M-to-Vent-Damper-Plug-On-Boiler-Control-Modules?gclid=CjwKCAjww5r8BRB6EiwArcckC9XS6Ca7rnYDUwHmBjxigc_GiMUQCjkGz8C9Goed3nzPJvM-M5wXOBoCU3gQAvD_BwE

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Precaud
    Precaud Member Posts: 370
    Dear Sir @EdTheHeaterMan , no worries, I work with electronics every day and hooking this thing up will be one of the simpler jobs I'll do all year.
    1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
    EdTheHeaterMan
  • Precaud
    Precaud Member Posts: 370
    Damper installed and works great. Fired up the boiler for this winter blast we're having, and what a diff it makes - basement is really too warm now. Not a bad problem to have...
    1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
    ethicalpaul
  • PMJ
    PMJ Member Posts: 1,266
    Precaud said:

    Damper installed and works great. Fired up the boiler for this winter blast we're having, and what a diff it makes - basement is really too warm now. Not a bad problem to have...

    They are absolutely huge with regard to efficiency. Running without one is really doing it the hard way.

    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
    Precaud
  • They are absolutely huge with regard to efficiency. Running without one is really doing it the hard way.

    I had always heard that it's what manufacturers had to do to get their equipment from 79% to 80% efficiency.

    It stops heat from going up the flue, but heat is still lost out of the draft diverter. Definitely not as fast.

    The replacement of a defective damper will wipe out all savings.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Precaud
    Precaud Member Posts: 370

    It stops heat from going up the flue, but heat is still lost out of the draft diverter. Definitely not as fast.

    So is it necessary to keep the draft hood as a safety backup?
    1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.
  • PMJ
    PMJ Member Posts: 1,266
    edited October 2020

    They are absolutely huge with regard to efficiency. Running without one is really doing it the hard way.

    I had always heard that it's what manufacturers had to do to get their equipment from 79% to 80% efficiency.

    It stops heat from going up the flue, but heat is still lost out of the draft diverter. Definitely not as fast.

    The replacement of a defective damper will wipe out all savings.
    Can't agree there. Time to steam is what is important. Efficiency is net steam delivery at the rads/unit of burn time. No damper will lose minutes in this department every single cycle as an open flue will cool the boiler that much. It isn't just about what goes up the flue with the boiler off. It is more about the extra minutes of burn time needed to deliver the same amount of steam where you want it. Adds up to a lot of extra minutes burning to reheat that boiler so it can steam at all while you deliver nothing.

    I would pay extra for these just to have more even heat. But I bet the math works anyway.
    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control