Another near boiler piping

Options
gennady
gennady Member Posts: 839
Still in progress




Comments

  • ethicalpaul
    ethicalpaul Member Posts: 5,704
    Options
    I don't like the main supply coming off a horizontal from the header like that (if that's what I'm seeing there)
    NJ Steam Homeowner. See my sight glass boiler videos: https://bit.ly/3sZW1el
  • Steamhead
    Steamhead Member Posts: 16,856
    Options

    I don't like the main supply coming off a horizontal from the header like that (if that's what I'm seeing there)

    Agreed. That pipe should come off the top or at a 45° angle, to keep the steam from carrying water into it.