Triangle Tube Strange Problem
Rich Davis_2
Member Posts: 121
Fall servicing a TT PS 60, it wouldn't lite. Checked ignitor (new last year) along with the ignition wire, everything OK. Checked spark with a spark plug tester, great spark. By accident I restricted the air flow into the venturi and it lit. Thought that was odd. Checked propane press. 9"WC. Checked combustion the best I could get was CO2 was 10.1% and O2 3.1%, adjusting the screw didn't make big changes. I also checked the vent and air supply both clean. I can get it to operate normally if I put some tape over the intake tube to the venturi to partly block the air but, that ain't right. Any suggestions would be greatly appreciated. Thanks
0
Comments
-
It still sounds like a fuel/air mix problem.
Call tech. support at (856)228-8881.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
is there a check for combustion check at some other speed, like you set it at low speed but also has a spec for high speed or something like that?
An air leak or a bad valve will cause it to be correct under the condition that you set it but incorrect at any other operating point.0 -
I would suspect an issue with the venturi or burner. At O2 of 3.1% you are a little rich. Why it would ignite when you make it richer is a head scratcher.
This is a good question for tech support."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
my name is Ed Nelson I am in tech support at triangle tube
did you check the venturi and the pressure drop in fuel pressure at the point of ignition you shouldn't see more than a 1" drop
if we can be of service please call us at 856 228 8881
Monday - Thursday 8- 5 eastern time
Friday 8- 4:30
hope this helps
Ed2
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements