Pictures! Steam boiler cracked 8 years old, is this correct piping?

hello, my name is J. Walsh. I am new here. I have pictures and below is a description of what I believe I am looking at. steam is not my area of expertise but, I believe this loop of the Hartford is too low, (approx 18" to center ground up) has the wrong tee, and the header looks to low also. (Approx50-51 " from the floor but just 20" from the top of the boiler. This is a crown mod# KSZ075BOPZZPSU s# booo492539 series 8 17 2010 allegedly installed in 2012.90k btu net 68k. Becket burner. I do not see much rust tword the top of the boiler and it seems to be leaking about where the lwc is installed on the front tapping 24-26" from the floor. Installer used 3" pipe off the top and once it hits the ceiling seems to pitch away from the boiler a little. I have a picture where it can be seen but maybe not noticed with the eye.
What I would call the equalizer is 2" coming off of the main header with a 3 x 2 90 and drops directly down to about 3" from the floor with the hartford loop tee about about 18" above the floor as mentioned above. Thank you in advance for any help.

Comments

  • MasterBummerMasterBummer Member Posts: 6
    Pics if not attached. I don't see them,

    Sorry
  • MasterBummerMasterBummer Member Posts: 6
    More

  • MasterBummerMasterBummer Member Posts: 6
    6 of 8
  • MasterBummerMasterBummer Member Posts: 6


  • MasterBummerMasterBummer Member Posts: 6
    edited October 2
    8 of 8.

  • EBEBRATT-EdEBEBRATT-Ed Member Posts: 7,315
    Looks like it's piped ok if the elevations are correct
  • SteamheadSteamhead Member Posts: 13,998
    Agreed. I'd bet the system is losing water somewhere, and all that fresh make-up water caused the leak by rusting out the iron above the waterline.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • FredFred Member Posts: 8,440
    edited October 2
    The piping looks fine. The header should be about 24" above the normal water line so if it is 20" above the top of the boiler, it is fine. The Hartford loop looks good. I don't see a problem with that fitting. It is connected with a close nipple, as it should be. What causes you to say the boiler is cracked? If it is leaking at the LWCO tapping, it may just be a bad fitting there that can be replaced. It does look like a leak on the bottom of the Sight glass fitting.
    How much water is it losing? Do you see any water pooled around or under the boiler? Most of those boiler blocks have a ten year warranty so you may be able to get some proration on a new block or a new boiler, if, in fact the block is leaking and the house is still owned by the original purchaser of the boiler and whatever other hoops the manufacturer may want you to jump through.
  • ted_pted_p Member Posts: 63
    edited October 2
    Fred said:

    ... I don't see a problem with that fitting. It is connected with a close nipple, as it should be. ....

    I think the reason the Tee looks wrong to @MasterBummer is because the piping diagrams in the Burnham/Crown IOMs show a Wye with a longer nipple as the "preferred piping" where the close nipple normally connects to the equalizer; but they also show a Tee with close nipple as an approved alternate, so as you, @EBEBRATT-Ed, and @Steamhead have said, it's OK.

    Here's an example from the V8H manual:



    I'd be indebted to anyone who would explain
    Burnham's rationale for using the Wye at that location....
  • mattmia2mattmia2 Member Posts: 1,872
    Looks like maybe it wasn't cleaned frequently or had the burner adjusted correctly. Probably worth it to take the trim and the front panel off to see if there is really a crack or just a leaking fitting.
  • clammyclammy Member Posts: 2,531
    Maybe it’s because it has no swing joint ,piped w a single riser and most likely never skimmed or clean . That’s usually a prescription for short life span as is your case ,doesn’t look like pro installed Peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating
    CLambNew England SteamWorks
  • New England SteamWorksNew England SteamWorks Member Posts: 1,356
    Missing swing joint. What was the water consumption like?


    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • ethicalpaulethicalpaul Member Posts: 1,866
    I'd be indebted to anyone who would explain 
    Burnham's rationale for using the Wye at that location....

    Well to my mind, a wye is like the shortest possible connection there. It’s even closer than a close nipple. Probably doesn’t make any measurable difference 