Automatic vent damper reliability
I'm not going to do this if I can only count on 2-3 years of reliable operation. So the question is: How far is far enough?
Comments
-
I have an Effikal I just pulled from service that never gave me any trouble, you can have it for free if you want.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Can't say no to that... aren't you using it with your new Peerless? I'm curious, how far from your old boiler was it installed?1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.0
-
My apologies, it's a 5". It was mounted just above the Utica, directly above the exhaust box thingy.
The Peerless came with a new one mounted to it in the same area.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Thanks anyway, no problem. So yours was reliable mounted right at the boiler... hmmm.1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.0
-
Is it going on a Gas-fired boiler or an Oil-fired boiler?
Gas-fired boiler is ok for the most part. There are many manufacturers that are factory equipped with Effikal dampers, they are the most reliable. and you can install the damper as far away as you can, to increase the life of the unit. The further away, the cooler the flue gasses are... the cooler the flue gasses are, the longer the parts will last.
you still want to check operation each season snd inspect for rust, corrosion, and wire connections for good contact. I guess if it is too far away then condensation of flue gas in the connector pipe from the damper to the chimney base might add to the deterioration of the unit. I think that anywhere after the draft hood is acceptable.
Oil fired? I would stay away from using a vent damper. Shut off the flow at the burner. Wayne Blue Angel and Riello burners have such a devise built into the burner. There is even a discontinued damper from Beckett the worked on centrifugal force. If that fails Beckett says to discard it
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Mine was right on top of the drafthood for a few years and then I moved it away from it to install a barometric.
That being said......I never liked the motor and gearbox directly over the drafthood being cooked. Especially when the damper closes and the drafthood gets good and hot. I can't say if it's actually bad for it or not, but if I was building something from scratch I wouldn't put it there.
Mine is from 2011 and still working fine.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
2 -
Yeah, mine seemed to be from the same age as the boiler, about 1992 and it worked fine as long as I was its caretaker, the last 3 winters.Precaud said:Thanks anyway, no problem. So yours was reliable mounted right at the boiler... hmmm.
That area didn't really seem to get "cooked" on my boiler. Sure the gases going up the flue were hot, but I never noticed that surrounding area getting toasty (the motor is offset from the flue pipe of course and seemed to stay no hotter than "warm")NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I had a Field Controls unit I retrofit on my old boiler. Failed at 3 months old, but I moved it manually a couple times before I knew better. The replacement is 2 years old now and I transferred the motor to a new damper on my current used boiler. My tall chimney has such good draft that I don’t think it really gets cooked too much. Boiler room doesn’t get that warm really even in summer with my indirect firing it a dozen times a day.1
-
Effikal 10". at least 6 feet from draft hood. It is actually on the other side of a wall from the boiler. I installed it myself about 1996. I do 2-3 cycles per hour. Not one issue with it all these years.1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control1
-
Wow. Not bad.PMJ said:Effikal 10". at least 6 feet from draft hood. It is actually on the other side of a wall from the boiler. I installed it myself about 1996. I do 2-3 cycles per hour. Not one issue with it all these years.
1950's Bryant boiler in a 1-pipe steam system at 7,000 ft in northern NM, where basements are rare.0 -
motoguy128 said:I had a Field Controls unit I retrofit on my old boiler. Failed at 3 months old, but I moved it manually a couple times before I knew better. The replacement is 2 years old now and I transferred the motor to a new damper on my current used boiler. My tall chimney has such good draft that I don’t think it really gets cooked too much. Boiler room doesn’t get that warm really even in summer with my indirect firing it a dozen times a day.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
There were some issues when Field Controls bought Effikal. These seem to have been resolved, and we aren't seeing more than one or two damper issues per season recently.
Also, you can get replacement motors for Field and Effikal dampers (same unit for both) so there's no need to replace the entire damper. I think the part# is GVD-RMA.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
How often it cycles will also determine the life. If the boiler short cycles, so does the damper motor.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If the Pressuretrol is wired between the damper and the gas train, the damper will stay open if the boiler cycles on pressure.mattmia2 said:
perhaps a delay on close for the types f steam boilers where they cycle on pressure frequently?hot_rod said:How often it cycles will also determine the life. If the boiler short cycles, so does the damper motor.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements