Low temp radiant off of existing baseboard system

tk92
tk92 Member Posts: 4
Hi all I am looking for some help with installing a small section of radiant in my house. An additional was put on and I would like to put radiant in this room. The house currently has baseboard heat. I have been doing a lot of research but not sure of the best/simplest way to go. I came across the taco rmb-1 which seems like it would be a simple solution for reducing the temp for the radiant loop and would tie into my sr relay. When I look at the taco recommended piping the show p/s piping however that isn’t not how my boiler is currently piped. I’ve attached a picture of what I thought would be and easy was to hook it up but I don’t know if it will work. Thanks in advanced.

Comments

  • tk92
    tk92 Member Posts: 4
    I am also open to other ideas of stepping the temp down/controls just didn’t want anything overly complicated. 
  • Jamie Hall
    Jamie Hall Member Posts: 24,856
    Pretty much any mixing valve which would allow you to mix the return from the radiant with a feed from the boiler, the excess going back to the boiler. The problem is, of course, to get circulation in the radiant loop. You may need a separate circulator.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • tk92
    tk92 Member Posts: 4
    Yes I had looked at a simple 3 way mixing valve but would be sending cold water back to a non condensing boiler.
  • Jamie Hall
    Jamie Hall Member Posts: 24,856
    Eh? Well, cooler perhaps -- the rejected water from the radiant loop, which would have mixed with the return from the rest of the system... but seems to me that if that's too cool, you should be running primary/secondary on everything
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hot_rod
    hot_rod Member Posts: 23,392
    It depends on the size of that low temperature load in relation the boiler as far as if bit will pull the boiler return down for extended periods.
    If that radiant zone is 20% or less of the total load, you should be fine.
    You could connect and observe on a design day, typically you want the return up around 130F within ten minutes of boiler run time.
    Certainly no harm in adding a return protection valve. if you go that far, I'd change the piping to primary secondary or better yet use a hydro sep.
    Kinda depends on how involved you want to get? It is best to pull that low temperature load of a better piping arrangement.

    Here are some ideas for connecting a low temperature loop into a conventional boiler and high temperature distribution.

    https://www.pmmag.com/articles/84495-a-little-floor-warming-please-john-siegenthaler
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • tk92
    tk92 Member Posts: 4
    Thanks hot rod. This setup would be an easy way to add the radiant.I would assume the the 2 new circulator would be wired to both turn on the off the same time? 
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    The Oventrop Unibox does this easily, as long as the connected load is under 12K btu's.
    https://www.oventrop-us.com/unibox
  • hot_rod
    hot_rod Member Posts: 23,392
    Yes, both circulators need to run together
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream