I'm going to be replacing/moving a few old decorative cast iron radiators as part of a complete hot water heating system replacement. The existing piping is a mix of 1.25" and 1.75" iron, as well as 1.5" copper. Is there any reason not to replace all of it with 3/4" copper? I don't know if the increased water velocity through the pipes would be a good or a bad thing, or whether the greater water mass in the old piping is good or bad, or even whether it makes any difference at all.

Comments

  • Jamie HallJamie Hall Member Posts: 13,448
    You will have an additional head loss. Roughly 4 times the loss between the two copper sizes, and -- depending on the condition of the iron pipes -- any where from say twice the loss to 6 times the loss for the bigger iron pipe. This may throw balancing off, but otherwise -- assuming the pump(s) can handle it, should be OK.
    Br. Jamie, osb

    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.

    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch