AY1014 fan speed control
Would anyone be familiar with how the fan speed is selected for just fan, for heating or for cooling. I am not sure my a/c is using the high speed. The air handler is an AHG36-0A.
Thanks,
Serge
Comments
-
It would appear that it is selected with the dip switches.
Er, never mind. Those actually are resistors, i just saw the actual pictures. they looked like switches on the "schematic" which only shows the board as a black box, is not an actual schematic.
According to the schematic, high and low, red and black to the blower, are swapped.0 -
Looks to me like it is wired to run on low speed on cooling On the control board Black should be hi speed, red low speed and blue medium speed.
So you should be able to swap the black and red wires,
Red which is on high speed on the board, move the black wire to hi speed and the red to low speed.
Check with a meter to make sure only 1 wire (black, red & Blue) is powered at the same time. Hi speed black for cooling, Blue medium for heat and the red terminal on the board is probably dead the wire just parks there0 -
A/C typically powers the Hi speed terminal. However, Hi speed on the motor is Black. You're showing Red (Lo speed) in your pic.
Like the diagram shows:
Hi- Black
Med- Blue
Lo- Red
Switching the thermostat to "fan on", might energize a different speed.0 -
Thanks everyone. Would someone know how the control board knows if it is a call for heat or for cooling. I think the yellow wire from the thermostat is not even connected to the zone board in between the thermostat and the air handler. Fyi the air handler is mostly for a/c, heat is secondary as the main heating is radiant floor heating.
Thanks again0 -
Y is cooling, G is fan, W is heat. Typically a t-stat closes Y and G to R on a cooling call. If only G is connected, it will usually produce a low fan call in newer systems, which might be why the wires were reversed.0
-
Do you have the manual? Or download it? Comfort- Aire?
Or if you have a meter, you can check to see which terminal (Hi- Med- Lo) gets 120v on a heat call. Dip switches control the time delay.0 -
Thank you. Yes Comfort Air. The manuals i have or found does not mention anything on the fan speeds.
Serge0 -
Fan speed matters for air distribution of course, but in your case it should be set for speed and water temp to best match the BTU's needed to heat the space.0
-
Thanks again. As mentioned in an earlier post, it is used only for aux heat main heat is radiant floor heating. Its main function is for A/C and since my vents are in the floor ( because added to old house) I want to make sure for A/C I am using the highest speed.
Serge0 -
I tested the three leads high low medium and getting 120, 70 and 100 respectively with just the call for fan. Same when A/c starts. Since all the lead seem to be outputting what does this mean and what is the impact of the reversed red and black leads.
Thanks
Serge0 -
the terminal on the board with 120v is the one that is active. the voltage you are measuring on the other ones is flowing through or being induced from the motor.0
-
Pull the three fan leads off the terminals & turn the thermostat to each setting to prove which terminals are energized. Turn the condenser off to avoid causing issues due to no airflow across the coil. Plug them back in according to the speed you want, using the table in the schematic to determine low/med/high. A wye cable can be fabricated if you want two functions to have the same speed. Be sure to isolate any unused speed taps. Note that ΔT must be within acceptable range, some taps may not be useful.0
-
Thanks all, very helpful information.
Going back to an earlier post in the thread i mentioned the y wire going to the air handler is not connected to the zone board that is in between my t-stats and the air handler. The y wire from the zone board is going directly to my heat pump and not the air handler. Any ideas why? Should the y wire ve connected to give more speed options say low for fan only, high for a/c and medium for heat.
Serge0 -
Switch the Black and Red leads. Hi speed terminal on the board to Black, Hi speed fan. Don't worry about the other voltages.
I don't know why they didn't connect to Y on the board, but it has no effect on fan speed unless your thermostat is capable of setting "fan on" to Med or Lo.0 -
Yes. I would extend it to the air handler & land it appropriately. It appears that the control board has a freezestat that will shut off the compressor if the coil starts to freeze. This is a nice feature that I personally would use. It entails landing the Y call from the thermostat & the compressor command on two separate terminalsmattmia2 said:but if the thermostat is connected to g instead of y, isn't the thermostat making a fan call instead of a cool call?
I would imagine that the board will give different fan speeds for the three different calls, but I can't be sure without a manual. You can relabel the three fan speed taps with what energizes them, that would make setting it up a little easier.
0 -
Thanks Ratio.
I connected the thermostat y to the air handler and it did not seem to change the speed, the y was sending a 24v. So would it be normal that the fan is only controlled by g and the added y call does not change anything... It is pretty hot so i won't test the call for heat from my heatpump right now to see what call for speed it gets.
As for the freezestat, the y going to the compressor ( i am the assuming heatpump) is cut before leaving the air handler and instead the y to the heatpump is coming directly from the zone control between my thermostat and air handler. Could the y to the heatpump come from the air handler instead of the zone control.
FYI, the original installers had a lot of problems setting my system up, with many issues after the install, I had some problems with the a/c not working and may explain the unconnected y. Anyways this is the reason i am trying to understand how it works.
Thanks for all the help everyone,
Serge0 -
Ok, I found an IOM for that unit here. It says on page 3 (page 4 of the pdf) section G. that Terminal number 4 on the fan relay (FR) is the cooling blower speed and terminal number 6 on the fan relay (FR) is the heating blower speed.
That doesn't appear to match the picture of the control board.
If you turn off the outdoor unit at it's disconnect, you can run the air handler in heat or cool without any issues. I think you're going to have to do that to figure out which terminal is energized for the various modes, unless there does happen to be a fan relay with terminals 4 & 6 on it.
0 -
> @ratio said:
> Ok, I found an IOM for that unit here. It says on page 3 (page 4 of the pdf) section G. that Terminal number 4 on the fan relay (FR) is the cooling blower speed and terminal number 6 on the fan relay (FR) is the heating blower speed.
>
> That doesn't appear to match the picture of the control board.
>
>
>
> If you turn off the outdoor unit at it's disconnect, you can run the air handler in heat or cool without any issues. I think you're going to have to do that to figure out which terminal is energized for the various modes, unless there does happen to be a fan relay with terminals 4 & 6 on it.
I dont think that's the same board.
@Sergea29, we now know the black motor lead is Hi speed and it connects to Hi on the board for A/C.
You mentioned heat pump but that unit has an integral hydro coil, so I'm confused.
Is this secondary heat source staged through the thermostat?
I'm not familiar with that zone board. Damper system on that air handler?
Bottom line, what are we trying to figure out now? You want to run Med or Low on heat mode?
The board in your air handler seems OEM and specific to that model. I cant find it on the ICM website. I noticed a Universal board shows AQ (Aquastat) can control the fan on a heat demand but it doesn't mention speed, and shows only one motor hot lead.
With AQ "ON", the fan will energize after the hydro coil aquastat closes, and sends 24v to AQ on the board. Whether that controls a different fan speed, I have know idea. But I'd like to find out. With AQ "OFF", the fan is controlled by the thermostat in heat mode.
A relay can be added to run a different fan speed for heat.0 -
Thanks. I am actually trying to get fan only at low and a/c at meduim or high. My main heating is radiant floor, the heatpump is only aux heat and yes through the thermostat ( ecobee). The hydro coil i believe is to defreeze my heatpump. I found this which show some more info on my board. The fan and a/c is high dehumid medium and heat low. I was thinking of trying to find a way to use the dehumid the set the speeds i want.
All the dampers are controlled by the zone board, Carrier.
Serge0 -
Looks like you'll need to do some relay magic to get a low speed fan-only G call out of the unit, as it said that G is high speed. Connect a spdt relay coil to the Y call, take the HI terminal from the air handler to the common of the relay, the low speed tap to the NC, & the high speed tap to the NO terminal. G will run the fan in low, Y will run the fan in high.
Verify the rating of the relay you're using.
0 -
Thanks. So no hope simply using the dehumid call?
What rating should i look for in the relay?
Serge0 -
The unit energized the 'HI' terminal for a Y (cooling) or G (fan) call, the 'MED' terminal for a dehum call, & the 'LO' terminal for heat. You want the fan on high speed for cooling & low speed for fan-only, right? How does it determine it needs to run in dehum? If there's a separate dehum terminal, try landing the fan call (usually green wire) on it & moving the low speed tap to the 'MED' terminal. Run it in all modes (including fan on [not in auto] with a cooling call) to make sure we didn't make it worse.
it's not clear if you use this unit for heat at all, if so, you may want to make a wye cable to run low speed for both dehum & heat call.
0 -
Thanks. I am away a few days and will update once i do the tests.
Serge0 -
Oh—forgot about the relay. If needed, you'll want a 24 VAC coil, single pole double throw (AKA form C), rated for at least the horsepower of the motor & twice that would be fine.0
-
Ok so tried the g call connected to the dehum terminal and nothing happens. I assume g terminal needs to be called as well. So using dehum won't work. The relay seems to be the only viable solution.
This is a bigger job so may not happen soon. I will update if and when it is done.
Thanks again everyone, greatly appreciated.
Serge0 -
Hello ,
So i got thr relay and ready to test things out. With regards to the relay, 1 and 3 are the coil. So yellow goes in 1 and 5 NC amd 3 is NO. High from the handler is in 4. I am seeing 120volts in 5 but when yellow is called nothing changes. Where should 3 go out to?
Sorry about the rookie questions.
Serge0 -
Is terminal 3 the coil, or the NO contact?
The coil will land on the 24VAC common (brown in the air handler) & the Y call (yellow). It should click when the cooling starts. The COMmon of the relay will land on the HI fan terminal (you'll need to make a jumper wire, use at least #14 gauge wire for it!), the wire that you removed from that terminal will go to the NC terminal on the relay, & the new speed you want to use for the cooling calls will go on the NO terminal.As long as there is no cooling call, the system will operate as before, but when the cooling comes on, the relay will switch the fan to the other speed tap.
Watch the temperature of the discharge air, you don't want it to drop much below about 55°
0 -
Thank you. Did get 14 gauge. No3 is the coil with 1. I have been using medium which was called doe fan and cool. With the new relay i will go to low for fan only and high for cool and use medium for heat call which rarely happens as the main heating is radiant floor heating. With medium I had check the air temp and it was safely above 55.
Thanks again,
Serge0 -
Everything is hooked up and working. I can't thank you enough.
I would have one last question. The medium terminal is going to to be unused. I am pretty sure only a dehumid call will activate it if at all and that won't happen, but should it be covered up somehow anyway. If so with what.
Serge0 -
You can put an insulated Sta-Kon on it (uncrimped) if you want, but those are generally left naked, nothing should be batting around loose in there.
Glad it's working for you.
0 -
Thanks!0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements