Troubleshooting hot water switching relay
Paul_85
Member Posts: 3
Trying to troubleshoot a "no hot water" problem. I think I have it mostly understood, just trying to figure out next steps. Hot water is fed from an indirect water heater connected to the priority zone of an oil boiler, using an Argo ARM-4P zone relay. Here's where I'm at so far:
I have time to figure it out - the only zone that will call for heat for the next couple of months will be the hot water heater, so keeping it on the ZC/ZR seems like it'll work for now.
- The hot water heater was calling for heat and firing the boiler (xx and ZC/ZR relays were lit), and boiler was firing.
- No power was being provided to the zone circulator - no light on the relay, and no voltage measured at the circulator.
- The circulator is fine - I switched the wiring to feed the circulator off of the ZC/ZR relay power and everything works as expected - circulator runs, hot water is back.
- It's not a persistent problem. Sometimes the zone lights up, and sometimes it doesn't.
- The relays themselves are fine, or at least appear fine. While the hot water heater was calling for heat and the relay light was on, I switched in all of the relays to the hot water heater zone. All of them lit up.
I have time to figure it out - the only zone that will call for heat for the next couple of months will be the hot water heater, so keeping it on the ZC/ZR seems like it'll work for now.
0
Comments
-
The most likely culprit is a loose connection … somewhere. If it's plugs, try unplugging and looking at all the pins and sockets and check for corrosion or overheating, then plug it back in. Otherwise -- make sure all connections are clean and tight. Make sure all wires are looking good.
If that doesn't work, are the relays plug in? If so, try swapping them.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If you jump T-T on the priority zone and are not getting 120v out of Zone 1 L & N, the relay is bad. You can order a replacement or switch it out from an unused zone.
If it does check out, then it’s the wiring.There was an error rendering this rich post.
0 -
Thanks very much to both of you, seems like something must be intermittently loose somewhere - the relays all work when I switch them into other zones and force them to call for heat. Appreciate the help...0
-
As a last resort, measure voltage at the "L" and "N" terminals for the indirect pump at the Argo control. If you have no power there, replace the control.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
This can be a pain in the A$$. Sometimes I remove the actual printed circuit board from the control case. Be careful if the control uses plastic standoffs, they can break and you will have a problem with reassembly. Observe the back of the PC board, look for burnt spots or areas where the solder may have been poorly applied. Over time the poor connection can overheat and melt the solder away from that connection. If you can carefully solder the bad spot, you can continue to use the repaired control.
This can be fixed with a small soldering iron and a drop of solder.
Trash this one
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements