Controls for hot water heat loop on steam boiler
I would like to replace the line voltage thermostat with a typical low voltage thermostat. I believe I can do that fairly easily by adding a Honeywell switching relay to the Taco line. But, I would also like the thermostat to turn on the burner when the Taco is running. I attached a wiring diagram of my system. Any recommendations for how to wire that?
Thanks in advance!
Comments
-
I'm not a steam expert but I would replace the Nest thermostat. Not a good choice steam or hydronic heat.
I think an aquastat would be the only control you would need.0 -
You can either add an aquastat that always keeps the boiler at a lower temp for the hot water loop or switch that aquastat and the pump with the themostat. You could use a relay off the pump to turn on the burner through that aquastat. Make sure the high limit from the steam side stays in series with the aquastat.0
-
Would something like the Taco SR502-4 2 Zone switching relay work? It looks like if I add that in between the 24V transformer and the thermostat, one zone can be set to turn on just the burner and the other can turn on both the burner and the circulation pump.mattmia2 said:You can either add an aquastat that always keeps the boiler at a lower temp for the hot water loop or switch that aquastat and the pump with the themostat. You could use a relay off the pump to turn on the burner through that aquastat. Make sure the high limit from the steam side stays in series with the aquastat.
0 -
KISS. Keep it simple... You have a thermostat which switches the circulator. Great. Keep it that way. Now add a strap on aquastat -- Amazon sells a good Honeywell version -- put it on the inlet to the hot water system from the boiler and wire it in parallel with the house thermostat. Set it to turn on if the water going to the hot water system is too cool -- you may have to fiddle with the adjustment. End of project.
On the Nest. Well, they can be made to work moderately well with steam. Defeat all the "smart" features -- particularly any setbacks -- and you will save fuel and money and increase comfort. If you can get far enough into its logic, set it for one cycle per hour...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
If I wire the aquastat in parallel to the 24V house thermostat, how do I also have it only turn on the system when the 120v circulator thermostat is also switched on? Maybe I'm not thinking it through correctly.Jamie Hall said:KISS. Keep it simple... You have a thermostat which switches the circulator. Great. Keep it that way. Now add a strap on aquastat -- Amazon sells a good Honeywell version -- put it on the inlet to the hot water system from the boiler and wire it in parallel with the house thermostat. Set it to turn on if the water going to the hot water system is too cool -- you may have to fiddle with the adjustment. End of project.
On the Nest. Well, they can be made to work moderately well with steam. Defeat all the "smart" features -- particularly any setbacks -- and you will save fuel and money and increase comfort. If you can get far enough into its logic, set it for one cycle per hour...0 -
Well... if you want it to not run the boiler unless the circulator is running, that would be what is known as a cold start -- which is alright, so far as it goes, but if the boiler is cold it's going to take a while for the baseboards to do anything. Since the baseboards probably don't really need much more than 140 degree water, the boiler usually will be at that temperature anyway -- and certainly will be if it has been steaming recently -- and you don't want it to run if it's already hot.jbot81 said:
If I wire the aquastat in parallel to the 24V house thermostat, how do I also have it only turn on the system when the 120v circulator thermostat is also switched on? Maybe I'm not thinking it through correctly.Jamie Hall said:KISS. Keep it simple... You have a thermostat which switches the circulator. Great. Keep it that way. Now add a strap on aquastat -- Amazon sells a good Honeywell version -- put it on the inlet to the hot water system from the boiler and wire it in parallel with the house thermostat. Set it to turn on if the water going to the hot water system is too cool -- you may have to fiddle with the adjustment. End of project.
On the Nest. Well, they can be made to work moderately well with steam. Defeat all the "smart" features -- particularly any setbacks -- and you will save fuel and money and increase comfort. If you can get far enough into its logic, set it for one cycle per hour...
However, you can do that if you like -- what you will need is a relay with a 120 volt coil, the coil in parallel with the circulator, and normally open contacts in series with the aquastat.
Adds a mostly unnecessary layer of control, but that will work.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
> @jbot81 said:
> (Quote)
> Would something like the Taco SR502-4 2 Zone switching relay work? It looks like if I add that in between the 24V transformer and the thermostat, one zone can be set to turn on just the burner and the other can turn on both the burner and the circulation pump.
Yes, that will work. Say zone 1 is steam. Wire the Nest to Zone 1 on the SR502.
Wire the circulator and new low volt thermostat to Zone 2.
Run a low volt wire from XX onto the SR502 to Rh and W1 according to your drawing.
The only operating limit is the pressuretrol. There is no aquastat but the hydro zone should never run long enough to cause the boiler to make steam.0 -
It would work, but would be far simpler and less expensive to go with the aquastat or aquastat and relay option unless you really want to rewire that zone for 24v for some reason.0
-
You might want to look at this Sequence of operation logic:
The steam boiler operates on Nest thermostat as indicated on the factory diagram.
parallel to the nest thermostat place a second control configuration that will operate the circ pump and the burner on a call for basement heat.
if the boiler reaches the limit temperature set on the aquastat (maybe 160°) the burner stops. No steam is produced at that temperature so no heat to the steam radiators. once the call for basement heat is satisfied, both the circulator and burner stops.
If there is a call for heat from the Nest thermostat, then the water is already hot enough to circulate and heat the basement.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements