Wiring V8043F To a Taco ZVC404
HeatPav
Member Posts: 13
I am in need of help wiring my 4 Honeywell V8043F 1051 valves to a Taco ZVC404-EXP-4 controller. Would I hook this valve up as a 4 wire valve? If so, It looks like I would need to hookup terminals 1 & 2 on controller to TH (middle) & TR (right) and terminals 3 & 4 on controller to the End Switch? I hope I got this right. The zone valve controller has a Main TT and a Priority TT but the boiler only has one TT on it and I was wondering should I be worried if there is a call for both DHW and heat at the same time what would get the priority, if any. I would like to somehow give DHW priority but don't know how it could be, or even needs to be wired. I have attached the boiler and controller pdf files. Any help or thoughts would be appreciated, thanks.
0
Comments
-
Correct.HeatPav said:I am in need of help wiring my 4 Honeywell V8043F 1051 valves to a Taco ZVC404-EXP-4 controller. Would I hook this valve up as a 4 wire valve? If so, It looks like I would need to hookup terminals 1 & 2 on controller to TH (middle) & TR (right) and terminals 3 & 4 on controller to the End Switch?
And only the "Main End Switch XX" goes to the boiler's "Heat Demand TT". Leave the Priority End Switch XX unwired and turn the Priority dip switch on the Taco controller to the "on" position.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
Thanks for the fast reply, that is what I was hoping, thanks Alan for your help!. This should make my wiring simpler.0
-
Also why bother with Th Tr, no need to do that (unless you really want to do that)0
-
Is it still April 1st?GW said:Also why bother with Th Tr, no need to do that (unless you really want to do that)
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
No the Th/TR
not the TH and the TR, you kinda need those0 -
Gotcha'8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements