HTP 155 wall hung
ollie123
Member Posts: 2
hello All, im trying to raise the temperature on my boiler its a HTP 155 combi
when i go into the 600 programme mode it says the temp is set at 180f but the temp coming out when being called is 135f, how can i raise this? do i need to by pass the outside temp sensor??
when i go into the 600 programme mode it says the temp is set at 180f but the temp coming out when being called is 135f, how can i raise this? do i need to by pass the outside temp sensor??
0
Comments
-
180* is the high limit and that's the correct setting.
The actual supply water temp is controlled by the OutDoor Reset function. That may need adjusting, but NOT disabling.
Is the boiler keeping your house warm enough?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0