OK to downsize water heater?
I've been looking at the Rheem Platinum 40 gal 38K BTU unit - I assume efficiency has gone up in the past 10 years and I am not one to want to heat an extra 10 gal on standby but wonder if it will match the old heaters delivery. The spec sheet says it will work for 2-4 person hh and 50 gal is for 5 people+...
Thoughts? Also, are there any better alternatives to the Rheem Platinum 40 gal/38K BTU unit in the same price range?
Thank!
Comments
-
-
@malex
40 gallon should be fine for three people. Back to back showers or showers and washing machine could be an issue but if usage is reasonable you will have no issues. They have the same size burners so not much difference0 -
Hi, You might test flow from the shower head and if it’s over 2.5 gpm consider getting a 1.5 gpm head that has the Water Sense certification. If you switch to a lower flow head, you can go to the smaller heater with very little concern about running out.
Yours. Larry0 -
With the lower burner input, you may run out of hot water more often.
You are correct that water heaters are more efficient now. If that were my house, I'd stick with a 50-gallon unit.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Larry Weingarten said:
Hi, You might test flow from the shower head and if it’s over 2.5 gpm consider getting a 1.5 gpm head that has the Water Sense certification. If you switch to a lower flow head, you can go to the smaller heater with very little concern about running out.
Yours. Larry
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment2 -
Cast iron radiator behind JerryChrisJ said:Larry Weingarten said:Hi, You might test flow from the shower head and if it’s over 2.5 gpm consider getting a 1.5 gpm head that has the Water Sense certification. If you switch to a lower flow head, you can go to the smaller heater with very little concern about running out.
Yours. Larry
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
Clow gas steam my friend.hot_rod said:
Cast iron radiator behind JerryChrisJ said:Larry Weingarten said:Hi, You might test flow from the shower head and if it’s over 2.5 gpm consider getting a 1.5 gpm head that has the Water Sense certification. If you switch to a lower flow head, you can go to the smaller heater with very little concern about running out.
Yours. Larry
That's got a built in boiler.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
Thanks all - i'll consider sticking with 50 gal or suffer Kramer hair with the lo flow head... only on the wall will a Seinfeld meme turn into a conversation about Jerry's cast iron radiator...0
-
There is a thread about them on here somewhere from about 10 years ago.0
-
Basic atmospheric Tank water heaters have a little more insulation now but the basic burners haven’t changed in 20 years. About 75-80% efficient. But why are cheap. So no payback for fancy ones.0
-
> @mikeg2015 said:
> Basic atmospheric Tank water heaters have a little more insulation now but the basic burners haven’t changed in 20 years. About 75-80% efficient. But why are cheap. So no payback for fancy ones.
I'd be more concerned about the heat going up the chimney than the tank insulation or burner design. There's a ton of heat going up that pipe when the burner is off.
My power vented 50 gallon stayed impressively hot without power for 3 daysSingle pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
My power vented 50 gallon had a ton of standby loss compared to my Superstore.
Conventional gas and electric water heaters used to be cheap, but between the price of metals and oil skyrocketing and requirements to suppress ignition of vapors they are about triple the cost of what they were 20 years ago and making alternatives competitive.0 -
We replace a lot of parts on power vents. The increase in installed cost probably results in about a 8-10 year payback or longer. Not really worth it in my opinion. A good option for new construction or if you are avoiding reclining a chimney however.
0 -
-
> @hot_rod said:
> Hopefully those power venters are not PVC vented. The high temperature that migrates up after a burner off cycle can really cook the PVC. Perhaps the worse application of PVC for venting flue gas.
Both mine and my parents are done in PVC exactly as Bradford White said to in the manual and there's no signs of overheating.
I'm also almost positive the blower continues after the burner shuts down for some set period.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
Sure a post purge helps, may as well send more of your heating dollars up the flue.ChrisJ said:> @hot_rod said:
> Hopefully those power venters are not PVC vented. The high temperature that migrates up after a burner off cycle can really cook the PVC. Perhaps the worse application of PVC for venting flue gas.
Both mine and my parents are done in PVC exactly as Bradford White said to in the manual and there's no signs of overheating.
I'm also almost positive the blower continues after the burner shuts down for some set period.
It's the glue joint that can fail, hard to see and predict that. The flue gas temperature in that center flue water heater is well, well beyond the 140F PVC temperature rating. Mod cons don't generally produce much over the operating temperature of the boiler. If and when they do, time to clean the HX
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
> @hot_rod said:
> (Quote)
> Sure a post purge helps, may as well send more of your heating dollars up the flue.
> It's the glue joint that can fail, hard to see and predict that. The flue gas temperature in that center flue water heater is well, well beyond the 140F PVC temperature rating. Mod cons don't generally produce much over the operating temperature of the boiler. If and when they do, time to clean the HX
The blower mixes cool air in to cool the exhaust.
The joints are solvent welded. Why would they fail before the pipe?
Regardless in my case and my parents I'm not concerned. We both keep an eye on things and would likely catch it early.
When I replace my heater if they call for a different material I'll use it otherwise it's staying.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
The power vent part outlasted the tank at about 18 years although it was starting to sometimes go out for reasons i didn't want to figure out. Everything looked ok with the burner and the connections and solder joints on the control. i decided it was time to work on the boiler project more quickly when that started happening.
The PVC did not look so great.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements