Teledyne LAARS propane ENDURANCE boiler
DaveJr_MayersHeat
Member Posts: 3
in Gas Heating
Good afternoon all, I went to a call last night for a banging noise that a home owner's Teledyne LAARS propane fired direct vent boiler was making. It sounded as though it was percolating but the boiler maintained a pressure of 18 to 20 psi and reaching a max temp of 199 degrees Fahrenheit. ( or so the read out said.) The relief valve, system can vent, expansion tank, and backflow feed were replaced within the past year. I could not replicate the issue while on site and according to the H.O. it is an intermittent issue. I monitored the operation while all 4 heating zones were operating as well as operating only one zone only and the boiler had seemed to function as it is supposed to. I am no expert with this brand of boiler and was only able to apply what basic hydronic heat knowledge I have and no air seems to be in the system and no over pressuring issues were apparent. I am looking for some input to see if I am missing anything and/or input from others that are more familiar with this type of system. I have also attached a few photos of the boiler as well as a video of the sound it was making shortly after I left for my next call.
Thank you in adavance,
David M. Jr.
https://streamable.com/4utyi
David M. Jr.
Banging noises are usually an indication of water flashing to steam when there's not enough flow through the heat exchanger to pick up all the heat being generated.
Check the amp draw of the pump to make sure it's within spec's. Check the wiring connections at the pump as well.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab2 -
- 119 Geothermal
- 394 Solar