Odd problem with Luxaire (York) gas furnace.

stretch5881
stretch5881 Member Posts: 11
Luxaire 98% modulating gas furnace installed in 2010. I get an intermittent code for "pressure switch closed", 2 red flashes. This only happens when the temp outside drops below 0. I have found that a bead of condensation blocks the hose to the lower pressure switch. I blow the water out of the hose and then it runs fine. When it's that cold out, I need to run the furnace with the front cover off to prevent the condensation. The hose in question is the square hose with the curl in it.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,477
    @stretch5881

    That's good troubleshooting, not sure what the fix is. Somehow you have to keep water out of that tube
  • Ironman
    Ironman Member Posts: 7,550
    It sounds like you may be getting some flue gas recirculating into the fresh air intake. Can you post some pics of the vent termination and piping?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • stretch5881
    stretch5881 Member Posts: 11


  • stretch5881
    stretch5881 Member Posts: 11
    In the first pic, the pipe on the left is the exhaust.
    In the second pic, the pipe on the left is the intake.
  • stretch5881
    stretch5881 Member Posts: 11
    Ironman said:

    It sounds like you may be getting some flue gas recirculating into the fresh air intake. Can you post some pics of the vent termination and piping?

    Thinking about it even further, the wind was out of the west at over 10mph yesterday and this morning when it coded.
  • Ironman
    Ironman Member Posts: 7,550
    That actually looks pretty good. Some manufacturers are now recommending using a 45* Ell on the top of the exhaust termination, instead of a 90* Ell blowing straight out. There's less chance of exhaust gas recirculation with the 45.

    I'd also see if you can get the pressure switch hose to have an upward curve in it (inverted trap) to help prevent moisture from going into it.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    stretch5881SuperTech
  • stretch5881
    stretch5881 Member Posts: 11
    I'll try the upward curve and see what happens.
  • stretch5881
    stretch5881 Member Posts: 11
    All good this morning, but may take a week or two to see the result.
    SuperTech
  • HVACNUT
    HVACNUT Member Posts: 6,331
    edited February 2020
    If it happens again, try removing all hoses. Clear them out and the bung holes they attach to. Also check/ clear the main drain, trap, condensate pump, etc.
    I could be just periodic.
    Combustion is not 100%. The little Gremlins find a way to haunt you.
    I have to do it at my out-laws house every other year. And theirs is concentric out the roof.
    stretch5881
  • stretch5881
    stretch5881 Member Posts: 11
    Will do, thanks.
  • Henry
    Henry Member Posts: 998
    I have a York that had a similar problem. I modified the hoses to prevent any kinks. 6 months later, York had a recall as the hoses were too long.
  • stretch5881
    stretch5881 Member Posts: 11
    Since following ironmans' suggestion on the upward curve of the hose, there have been no hiccups. It's running better than it ever has since installed 10 years ago.
    Ironmanrick in Alaska