oil burner lockout help!
grye
Member Posts: 90
Hi Everybody..
It's beautiful today, but a cold front is fast approaching... which means now is when my boiler decides to fight me.
The issue: It keeps locking out. It's a genisys 7505, it will run for a little bit but then lock out, and need a hard reset to start again.
I'm pretty mechanically inclined, but usually don't mess with heat since I have young kids. The problem is, most of the reputable techs are booked up because of this cold front.
Are there any simple items to cross off my list to attempt? It's a one pipe steam system with the oil burner.
Thank you, be safe!
It's beautiful today, but a cold front is fast approaching... which means now is when my boiler decides to fight me.
The issue: It keeps locking out. It's a genisys 7505, it will run for a little bit but then lock out, and need a hard reset to start again.
I'm pretty mechanically inclined, but usually don't mess with heat since I have young kids. The problem is, most of the reputable techs are booked up because of this cold front.
Are there any simple items to cross off my list to attempt? It's a one pipe steam system with the oil burner.
Thank you, be safe!
0
Comments
-
Could be many things.
if your unit has not been serviced for a while you could change the oil line filters and the nozzle. This may fix it but you should still have a tech come and look it over.
That being said
You mentioned you have kids, and a safety device on your boiler in sensing a dangerous situation and protecting you and your family from harm.
If you are not comfortable working on your boiler, than don't. it only takes one turn of a wrench to turn your boiler into a Carbon Monoxide generator and put everyone in danger.
0 -
If it starts and runs for a bit (how long is a bit?) it is more likely to be either a problem with the oil feed or pump giving an unsteady flame, or with the flame sensor not seeing a good flame. Neither of these problems are really something I'd recommend a home owner to fuss with, but your oil company should have an emergency/no heat service which could help, assuming you are a regular customer.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
So I happened to get an oil delivery today (I was at about 1/4 of a tank)... and on a hunch I bled the line (didn't need to be bled, but I did anyway and there were no bubbles), restarted it, and it seems to be working fine (i'll delete this comment if i'm proved wrong!)
So here's a question... My boiler sits on cinderblocks. My tank, on small 6 inch looking legs. Plus it looks like there is a grade on the floor, with the oil tank being higher than the burner.
Are these gravity fed? As in, is it possible that I still had 1/4 tank of oil but since the tank is higher than the boiler it wasn't getting enough oil?0 -
Not gravity fed. The fuel unit on the burner does the job of moving the fuel from the tank through a fuel filter through a copper fuel line to the burner. Filters block up. Fuel unit strainers can block up and nozzles can block up.
That gensys control should be able to tell you where the fault is. I forget the routine for retrieving the data. google should help. That said. You should call your fuel dealer and ask for service. The combustion side of the system is nothing to tinker with.Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker0 -
No, they are not gravity fed. It's common to see the oil line come out of the top of the tank, across the basement ceiling and back down to the burner. The oil pump that you bled oil from pumps the oil from the tank. It's best to avoid fighting gravity when possible, but not 100 percent necessary.0
-
You need a competent tech with the proper tools and training.
Many things are possible, but it's out of your skill set to test/fix them.There was an error rendering this rich post.
0 -
@grye
It's possible you have a dirty filter or pump strainer and the burner was not getting oil properly. Filling the tank may have made the oil easier to get to the burner "fixed" the problem but you still need to have the problem looked at0 -
You all were right (shocking!)
Unit locked up again. Next (and easiest) item to try is the filter?0 -
> @grye said:
> You all were right (shocking!)
>
> Unit locked up again. Next (and easiest) item to try is the filter?
Yeah, if you are really that hesitant to call a professional the only thing I recommend checking out is the oil pump strainer and the oil filter. If you have some automotive brake cleaner I recommend spraying all the sludge buildup out of the filter canister. You can also use this to clean off the strainer in a pinch. But it's usually a good idea to have a replacement in case it's really plugged up, or if you tear the gasket.
The oil line could be plugged up, the electronic igniter or ignition transformer could be on the way out, the nozzle could be plugged. It's really a good idea to get someone who can do a complete evaluation of the entire system, and make sure the system is safe, reliable and efficient.0 -
Last time it ran for an hour before locking out. This time it only ran for a minute or two. Flame lit, it ran, then shut off. Then the next cycle the flame didn’t light. I reset it again, I can hear it kick on, but no flame.0
-
I should mention the boiler was serviced this winter. Cleaned, changed the nozzle, and changed the oil filter.0
-
-
-
If there is no ignition but there is fuel you are delivering fuel to the chamber where it will sit. If it does ignite on a subsequent try all that unburned fuel is going to light at once. That's a big deal and needs to be avoided. I would not reset it any more.Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker2
-
-
-
Thank you everybody. I replaced the filter, that didn’t do the trick. Then I bought a new pump strainer, and when I saw the old one I knew that had to be the issue. New strainer and she’s running. Good as new. Be safe everybody.0
-
@grye, do I understand that the filter in the oil line was OK, but the strainer in the fuel unit ("pump") was plugged?
What kind of oil line filter is it?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements