Tom_133
Member Posts: 910
Good Morning all,
I am being tasked with swapping out an old taco inline pump and replacing it with a new high efficiency.
I want to size the new pump but only know the Indirect is 500 gallons, Taco, ASME, and has 3" inlet on the coil. The old pump which seems oversized due to the delta being 4-5 degrees gives me some hints but not enough.
I would really like to get a pump I can reuse this summer when I replace that big ASME tank with 3 smaller indirects to save the customer some coin.
Anyone know where on the insulation I can cut to find the tag on the tank?
Or the pressure drop through the coil? Which seems unlikely due to the endless possibilities.
I am being tasked with swapping out an old taco inline pump and replacing it with a new high efficiency.
I want to size the new pump but only know the Indirect is 500 gallons, Taco, ASME, and has 3" inlet on the coil. The old pump which seems oversized due to the delta being 4-5 degrees gives me some hints but not enough.
I would really like to get a pump I can reuse this summer when I replace that big ASME tank with 3 smaller indirects to save the customer some coin.
Anyone know where on the insulation I can cut to find the tag on the tank?
Or the pressure drop through the coil? Which seems unlikely due to the endless possibilities.
Tom
Montpelier Vt
Montpelier Vt
0
Comments
-
Tom,
It would help us identify the existing circulator if you stood back a few feet and shot the veloute/bearing assembly.
I'm guessing the original designer wanted to transfer the energy to the tank real fast as DHW demand often needs to met almost instantly. Without more data, my guess is the pump is a Taco model 1612? This data sheet may help.
http://apps.taco-hvac.com/uploads/FileLibrary/1600Series_300-1.1_rev1.pdf0 -
-
-
It would help to know the model of the indirect coil. From there you will know required flow rate and head loss.
There is usually either a plate on the face of the coil or on the edge where it mates to the tank.
You are wise to suspect the pump is oversized. It is better to check the math than to just replace 1 for 1."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Well guys, I heard back from Taco, and they feel the same as me, I can probably throw a VR15 in and set it to what I want it to do for me. When I pull that big monster tank I will take a pic of the tag after I strip the insulation and update this post. But dont wait up, probably 3-4 months away. ThanksTom
Montpelier Vt1 -
probably work backwards, 3" coil 1/2 hp circulator, that would give you some idea of possible flow rate.
Don't get hung up on delta, it could start wide with a cold tank, and close down as the tank approaches set point. Hot to cold, rate of transfer is, has to be, ∆T driven.
An example of why you would not want to run a constrained T pump. Let the ∆ move. ∆T is an indication of heat transfer.
Watch how a wood boiler heats a buffer, or an indirect heating up, big gains on a cold tank, the last 10- 15° seems to take forever. ∆ closes, rate of transfer slows.
This applies to tanks, fin tube, radiant loops, air coils, even air to air, really any heat transfer.
https://www.caleffi.com/sites/default/files/coll_attach_file/idronics_23.pdfBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements