Weil_McLain Ultra 105 Boiler

cpft1
cpft1 Member Posts: 7
Had a new Weil-McLain Ultra 105 Series 3 boiler installed November 3, 2017. We use propane. Worked great for two years. On December 23, 2019 it wasn't maintaining temperature. Repair guy,who installed it, came and looked at it and couldn't figure out what was wrong with it. He talked to tech support and was told it needed a clean-up kit and to set it at high altitude setting until he got the clean-up kit. Repair guy returned on December 30 and installed the clean-up kit. Worked great until January 10, 2020 when it was not maintaining temperature again. Repair guy once again could not find the problem. He called tech support again and was told to set it at high altitude setting and leave it there because for some reason it required more oxygen. That is where it was left.
My question is, why did it work great for two years with no problems and now it needs more oxygen? To me it seems that some part must be failing to cause this.
Any ideas?

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Anyone do a combustion analysis, incoming gas pressure, check the inlet for debris (rare but possible) etc.
    Circulator moving water (not just 'running')?

    There was an error rendering this rich post.

    Zman
  • cpft1
    cpft1 Member Posts: 7
    The repair guy was here for several hours. I do not know what all he did. I do know that he checked the inlet valve and talked to Weil-McLain tech on phone.
  • Zman
    Zman Member Posts: 7,611
    You need to find out if they did a combustion analysis and get the results if they did. You will never get to the bottom of this without one.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    mattmia2
  • HVACNUT
    HVACNUT Member Posts: 6,338
    edited January 2020
    Agree with all above.
    WM does not allow adjustments to the gas valve on the Ultra without tech support and the combustion test results.
    The contractor menu would allow the tech to view history, check diagnostics, and put the boiler into manual test mode for low, medium, and high combustion numbers.
    Pop out the flue temperature sensor and insert probe. What could be easier?

    Out of curiosity, what is the elevation where you are?
    STEVEusaPA
  • Tom_133
    Tom_133 Member Posts: 910
    I also want to know your elevation, and how is the intake air piping look? Possibly plugged outside or inside somewhere? Ive seen dead animals, frozen, and other weird things in the piping that blocks the amount of air. A test to see if its in the intake air pipe would be to remove the door on the boiler to allow air from the room in. If the boiler comes up to temp, then you got a blockage. I had a different boiler do the same thing when it had a snowball stuck in the intake air piping outside, so go out and make sure thats all good. If when you pull the door off the boiler it ramps right up, you know where the problem is.
    Tom
    Montpelier Vt
  • DZoro
    DZoro Member Posts: 1,048
    Gas pressure should be checked, static and operating pressures. Regulator can be sticking at times.
    Along with all the above.
    D
  • cpft1
    cpft1 Member Posts: 7
    The elevation here is 626.64 feet.
  • cpft1
    cpft1 Member Posts: 7
    A combustion analysis was done. Intake is clean. Our elevation is 626.64 feet, so why would it need to be set on high altitude?
  • sallaberry
    sallaberry Member Posts: 19
    Well I would say a bad batch of propane when did they deliver compared to the problems occurring.
  • cpft1
    cpft1 Member Posts: 7
    We received propane on December 12 and the problems started around December 23. If it is the propane, what should be done?
  • Zman
    Zman Member Posts: 7,611
    cpft1 said:

    A combustion analysis was done. Intake is clean. Our elevation is 626.64 feet, so why would it need to be set on high altitude?

    Can you get the results of the analysis? Jus because it was done does not mean it was done right.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • cpft1
    cpft1 Member Posts: 7
    We received propane on December 12 and the problems started around December 23. If it is the propane, what should be done?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    @cpft1

    This type of equipment is fussy. Can't troubleshoot a problem like this without a combustion test. We need to see the #s
  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    When my W-M Ultra3 80K boiler was installed (I read the manual), the installing contractor did not do a combustion test. He looked at the fire through the window. He said the combustion was set at the factory. That is not what the installation manual said.

    It might even be true that the combustion was set at the factory, at the altitude of the factory (that might not have been the same as mine) and at the gas pressure at the factory (that also might not have been the same as mine. My guess is that it was pretty close, because when the one-year inspection time came, I had to dismiss that contractor for incompetence and I got a new, much better one. He did it correctly and did use a digital combustion tester and it was very close. But at least he knew it.

    After a few years, his company (he was not an owner) decided not to do residential work anymore, so I am now on my third contractor who I found on this web site. That contractor also has done work for some friends of mine. He knows what he is doing, always comes prepared (with needed kit), has obviously read the manual, and knows what his digital combustion analyzer is for and uses it every time.

    https://heatinghelp.com/find-a-contractor/detail/shane-a-foster-plumbing-and-hydronic-heating
  • Grallert
    Grallert Member Posts: 780
    service can't be done without an analyzer, knowing how to use it and what the numbers mean. A printed sheet should have, might have been left on the boiler for you and for the next tech who comes along. Lets see those numbers. They could lead to the solution.
    Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker
  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    service can't be done without an analyzer, knowing how to use it and what the numbers mean. A printed sheet should have, might have been left on the boiler for you and for the next tech who comes along.


    My current contractor always leaves me the printed slip his combustion analyzer produces. I keep all of them in an envelope along with my boiler instruction manual.
  • cpft1
    cpft1 Member Posts: 7
    We never received any thing other than a bill. There is not another authorized repair location within a hundred miles of us.