Defective Gorton valves?
Dollr
Member Posts: 35
Installed a brand new Gorton #C and #4 on 2 radiators today. Through 3 heating cycles neither of them has closed. They just hiss steam till the boiler shuts off. Only close if I slapped them. Can’t be how they’re supposed to work. Send them back? Thanks.
0
Comments
-
Are the radiators hot all the way across? No vent closes if the thermostat is satisfied before the radiator needs to get hot all the way across.0
-
> @Fred said:
> Are the radiators hot all the way across? No vent closes if the thermostat is satisfied before the radiator needs to get hot all the way across.
They said they hiss steam.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
All my Hoffmans on the other radiators close as normal. It’s my first time using Gortons. Thought I’d try them. Some say that they are quieter. Got them at Supply House. Think I’ll trade them back in for Hoffman’s. I don’t mind the click. It’s the sound of comfort! Thanks for your comments.0
-
You can hear vents blow/his air if the pressure is high enough, especially with large rads that have a lot of air in them.ChrisJ said:> @Fred said:
> Are the radiators hot all the way across? No vent closes if the thermostat is satisfied before the radiator needs to get hot all the way across.
They said they hiss steam.0 -
> @Fred said:
> (Quote)
> You can hear vents blow/his air if the pressure is high enough, especially with large rads that have a lot of air in them.
Fred,
Steam my friend.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I don't know @ChrisJ . The one time I had a Hoffman vent stick open, I could actually see the steam plume condensing in the air, out of the top of the vent. Just seems to me that if it is really steam, you'd see it condensing.ChrisJ said:> @Fred said:
> (Quote)
> You can hear vents blow/hiss air if the pressure is high enough, especially with large rads that have a lot of air in them.
Fred,
Steam my friend.0 -
> @Fred said:
> (Quote)
> I don't know @ChrisJ . The one time I had a Hoffman vent stick open, I could actually see the steam plume condensing in the air, out of the top of the vent. Just seems to me that if it is really steam, you'd see it condensing.
Yes,
That's why they said steam.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
Yup, it’s really steam coming out. Thanks guys.0
-
I had bad luck with a couple new Gortons last year. They were corroded on the seat, float, and body (White “barnacles”) and had to have a concussive adjustment just like yours to close.
They were C’s from Supplyhouse, now fully cleaned and modified as experimental 0.3mm orifice units that work flawlessly. None of the other Gortons I have obtained had this issue right out of the bag.0 -
”concussive adjustment“ love that!0
-
I had issues with Gorton's not closing within the past year, would gurgle through the end of the heating cycle even though the vent was steam hot. Tapping made them close, I tried adjusting their tilt to have them vertical which helped but swapping them out was the option that worked.0
-
Just for curiosity's sake, give a Maid O Mist from Supplyhouse a try. You can get 1 for 1/3 the price of a Gorton. If the same thing happens you can be pretty sure it's not Gorton's fault, whatever is going on.
As much as you hear me push the convenience, price and reliability of my MoM's even I think there must be something else at play for Gortons to be failing like this.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Gorton is pretty good about handling issues like this- give them a call.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Thanks for the advice, appreciated. I put a Hoffman #40 on from my “archive”. Functions as it should. I’m going to trade in the Gortons for 1-A’s. Thanks0
-
> @Dollr said:
> Thanks for the advice, appreciated. I put a Hoffman #40 on from my “archive”. Functions as it should. I’m going to trade in the Gortons for 1-A’s. Thanks
I had 12 new 1As. They all got swapped out for Gortons back in 2012 due to endless fun..Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Understood. I have 5 1A’ on other radiators for the last 6 years without problems.0
-
If you like them and they work for your system I can understand making that decision. Nothing wrong with that.Dollr said:Understood. I have 5 1A’ on other radiators for the last 6 years without problems.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I like the Hoffman’s but tried to experiment with the Gortons. They are probably perfectly fine vents. Just didn’t work for me for whatever reason. Thanks to all for the comments. Great community.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements