Radiant heat questions
Comments
-
Thermal image appears to indicate that one of the loops is not getting as much flow as the one next to it. OR if your loop is too long the warmer area is the beginning of the loop and the cooler area is the end of the loop.
What is your loop length? how long has the water been circulating when the thermal image picture was taken?Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
All loops are less then 200' 1/2 pex, the heats been on all day well at least the thermostat I never checked though maybe the loop is closed at the manifold0
-
The first picture shows the manifold that feeds that floor0
-
are you saying the pic number https://us.v-cdn.net/5021738/uploads/editor/mu/9zkdozly8daa.jpg is the same as thermal pic?
if yes, then you have insufficient flow in the loop that is cooler. 200 ft is no problem. see if the manifolds have adjustable flow controlsEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
can you tell by your experience with the install that the cooler area is the end of a loop that is working fine at the beginning? OR is the cooler area its own loop?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
It's at the beginning and the manifold does have an adjustable flow control0
-
What picture of the tubing layout correlates to the infrared picture?
What is the insulation detail below if any?0 -
Picture number 7 it's an open basement not finished yet0
-
No insulation yet0
-
You are positive those two loop returns are not where the cool spot is in the infrared? Sure appears to be that way.0
-
Wich two loop returns are you referring to0
-
No insulation below... a big problem. the radiant heat is going down there. Long story... 6 years of oil burner service on a DIY radiant system ,and the basement was a sauna. Every year I told the customer to get the insulation finished. Also complained that the rooms above the uninsulated area were colder than the insulated areas. As part of a divorce, the house projects needed to get finished. Insulation suddenly was completed and WOW the problem rooms heated properly, POOF, like magic!
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
So this pic shows one of the Flowmeters is different from the others? May just be the angle of the picture. You need to double-check that
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
turn all loops but the one with no flow, see if it works then. Could be an air bubble in that circuit
Or lines crossed?
Certainly you need insulation, but all loops should get about the same S&R temperatures after they run an hour or so. They should all show a temperature difference between S&R maybe not exactly the same, depending on the circuit load.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Agree it’s a flow issue.
Is that ceramic plank style flooring, or hardwood in the IR pic0 -
It's ceramic tile , the gentleman who installed the boiler and all said I possibly need a bigger pump0
-
-
What model circ is installed on the problem loop(s). How many loops is that circ serving."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
It's a 007 serving 3 different manifolds about 1000' on each 4 zone manifold0
-
It looks like you have balancing valves and flow meters on the loops. What do they read?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
They say there's flow for sure, my educated guess would be air0
-
What are the flow rates reading at each loop on the gauges?0
-
The white caps on then upper manifold will shut off that circuit, are they all open? Looks like two are tightened down and two are loosened? Remove them all and the circuit is wide open.
Also on some manifold the clear plastic flow indicators on the bottom turn to adjust and balance flow, they should be backed all the way open. CCW if you face them them directly.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
CCW=Counterclockwise 😉0
-
They were all open I closed them to see if I can isolate the loop in question0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements