Hydronic radiant heat
Comments
-
-
Alan. Hydronic
We would need to know what controls it as far as thermostats and zone valves, and how it might all be wired up. There is a possibility the zone valve for your bathroom is stuck open , but is not sending a signal to the boiler. So what could be happening is when something else calls for heat, it also allows heat into the bathroom zone. So, check the bathroom zone valve.
Rick1 -
I have hot water with a nest thermostat. I’m not sure how to find out about valves0
-
Post some pictures of the boiler room. My guess is Honeywell zone valves with a failed end switch. When the bath zone calls it opens but does not fire the boiler, when another zone calls it fires the boiler and heats the bath zone."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
I opened up the picture and sucked air. What a conglomeration of a mess. I would hate to be the guy who has to work on any of that.
Anyway, turn up the thermostat for the bathroom and see if you have a corresponding light show up on the green Taco control box on the wall to the right. If the thermostat is working ok, and the Taco control box is working ok, you should have a light come on on the Taco panel, and the boiler and pump should come on.
Rick1 -
Thanks Rick! Yeah I just moved in and thought it looked a little crazy in the boiler room0
-
After you verify that the zone controller is working, you want to determine in the circulator is functioning. Sometimes you can hear it or feel the vibration. A change in the temp of the pipe is the best indicator.
This app is pretty trick but not completely fool proof. https://www.danfoss.com/en-us/about-danfoss/news/dcs/introducing-the-most-attractive-app-in-the-cooling-field/"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Do those magnetic indicators work on Tacos? Also they just indicate that the device is powered, they don't detect or indicate a spinning rotor. So limited use really.Zman said:After you verify that the zone controller is working, you want to determine in the circulator is functioning. Sometimes you can hear it or feel the vibration. A change in the temp of the pipe is the best indicator.
This app is pretty trick but not completely fool proof. https://www.danfoss.com/en-us/about-danfoss/news/dcs/introducing-the-most-attractive-app-in-the-cooling-field/
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Ok so the zone light turns on when I turn on the heat. The circulator sounds like a fan when I put my ear to it.. What app do I download? The magnetic one? Also I didn’t hear the boiler light.0
-
Also this is happening to my 3 rooms with radiant heat0
-
Are all the pumps wired to the Taco Zone contoler or just the radiant pumps? Might be the end switch relay in the Taco board or it is not wired into the Aquastat right.0
-
I’m not sure about all pumps. but I have a 3 zone Switching relay and a 1 zone.0
-
I stuck it on a grundfos the other day and it spun.hot_rod said:
Do those magnetic indicators work on Tacos? Also they just indicate that the device is powered, they don't detect or indicate a spinning rotor. So limited use really.Zman said:After you verify that the zone controller is working, you want to determine in the circulator is functioning. Sometimes you can hear it or feel the vibration. A change in the temp of the pipe is the best indicator.
This app is pretty trick but not completely fool proof. https://www.danfoss.com/en-us/about-danfoss/news/dcs/introducing-the-most-attractive-app-in-the-cooling-field/"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Still not working. I guess I need to get a heat guy in here0
-
Did it work before the nest came into play?
0 -
Before the nest it still wasn’t working correctly. My other bathroom has the original thermostat and works when it wants.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements