Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Sunrad valve type
mvagusta_2
Member Posts: 10
I have never installed one of these, are angle valves or the straight type preferred for single-pipe steam.
EDR is 25.
EDR is 25.
0
Comments
-
Whatever will provide the most room for fast steam and slow water to travel in opposite directions at the same time. A full-port ball valve would work if it's rated for steam (SWP = more PSI than that radiator will ever see). It doesn't need to throttle; just open and close.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Thanks, never thought of using a ball valve for steam.0
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements