Sunrad valve type
mvagusta_2
Member Posts: 10
I have never installed one of these, are angle valves or the straight type preferred for single-pipe steam.
EDR is 25.
EDR is 25.
0
Comments
-
Whatever will provide the most room for fast steam and slow water to travel in opposite directions at the same time. A full-port ball valve would work if it's rated for steam (SWP = more PSI than that radiator will ever see). It doesn't need to throttle; just open and close.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Thanks, never thought of using a ball valve for steam.0
-