Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Help restoring Hoffman System

2»

Comments

  • OatKing
    OatKing Member Posts: 20
    Happy New Year everyone! 
    Well it's been almost a year since I was last on The Wall.

    - I have isolated where the hammering is coming from - a Trane Concealed Heat convection unit. The way the unit was installed (in 1929) requires me to open the wall to check the slope. Not thrilled about tearing into our dining room wallpaper, my wife is even less so. 

    - I can't tell for certain if the system is loosing water or if water is delayed getting back to the boiler.

    - I spoke with a pipe fitter about next steps and we plan to open the return lines near the boiler and check for sludge. 

    - once I find out more, I'll pass along.

    - all the best in 2022!
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,248
    Also check that the boiler is not sending water up the chimney. Hope not
    cross_skier
  • Jamie Hall
    Jamie Hall Member Posts: 24,479
    The water should be simple -- note the level accurately when the boiler is cold some day. A srping clothespin works well, but there are other was. Then come back after the boiler has run for a while, or throgh a few cycles, and cooled down again. If the water level has dropped, you're losing water.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England