Open/closed system
fatalbert1
Member Posts: 3
I have a outdoor wood boiler which is an open system going to a new shop with infloor heat. It will be separated by a water to water heat exchanger because of elevation difference. There is a pump on the load side to move the water around but wasn't sure if I would need an expansion tank as well?
0
Comments
-
On the closed loop, pressurized side you willBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If an expansion tank isn't connected would the water temp and pressure build up from the pump cause a leak?0
-
If you are speaking of the closed side -- the side with the infloor heat, I presume, it's not the pump that's your problem. In a closed system, the water will try to expand as it warms up. Unless that expansion has someplace to go -- an expansion tank, perhaps, or in an open system a vented tank -- the pressures resulting from the expansion can be amazingly high. If you have a pressure relief valve, hopefully it will open before you have a problem. Otherwise, the system will fail -- catastrophically -- at the weakest point in the pipe or fittings.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
This.hot_rod said:On the closed loop, pressurized side you will
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements