Junk in sight glass

Msil1955
Member Posts: 12
Our steam boiler installer will be here shortly to skim and flush again. I've noticed that since the last skim session the pressure gauge never moves, and the low water cutoff LED goes on and off even though there's an inch and a half of water visible in the sight glass. Is it possible these controls need to be cleaned out. Also, the high pitched whine has become intermittent and changes in pitch.
0
Comments
-
It is possible that the top and bottom shutoff valves to the sight glass are closed. If closed, the level will not reflect the true boiler water level. Try opening and closing these valves and see what happens.
It is also possible that the water passage in the bottom fitting has become clogged. If it has, it will be necessary to turn off and drain the boiler to below the level of this fitting before the fitting can be removed and cleaned.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0 -
I would also recommend a "proper" valve on the bottom of the sightglass.
https://www.youtube.com/watch?v=OgKAO8s8QBE
All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
It's a Safgard. I've seen it run for longer than 20 minutes and the only time it shuts down is when the water level is 1 inch below the sight glass.0
-
Categories
- 120.9K All Categories
- 83.8K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 416 Carbon Monoxide Awareness
- 36 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 116 Geothermal
- 154 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 754 Plumbing
- 5.3K Radiant Heating
- 358 Solar
- 13.9K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 37 Industry Classes
- 70 Job Opportunities
- 14 Recall Announcements