Bell & Gossett circulator ID
Alan (California Radiant) Forbes
Member Posts: 4,243
Mike Sheppard, Scott Secor and Mr. Holohan helped me the last time I needed help with B & G. Here's another one. This pump is 65 years old and has died. The pump flanges are 8-1/2" apart, so it's not a Series 100 model. Must be a PR (high volume) or HV (high head) series, no? It serves an 8-loop manifold, 1/2" copper loops; no idea what the loop lengths are.
We figured out last time the the dead guy who did the installation probably oversized the pump and I think the same is true for here. A series 100, Taco 007 or a Grundfos 15-55 will probably do the trick.
Any comments?
We figured out last time the the dead guy who did the installation probably oversized the pump and I think the same is true for here. A series 100, Taco 007 or a Grundfos 15-55 will probably do the trick.
Any comments?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
This was on State Supply's site showing a replacement bearing:
"Bell & Gossett front bearing for B&G model 189101, 189102, 189103,189129, and 189163 bearing assemblies on series HV, 1, 1-1/2, and 2 pumps."
So that's probably an HV.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
The size and shape of the impeller is a good rule of thumb for determining a circulator type, narrow, large diameter impellers are typically high head, as a 3450 rpm motors.
Did those older 3 piece circulators ever use 3450 rpm motors, seems 1/6 hp 1750 is most common?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
These are higher flow lower head than Grundfos. We stock all the parts for our service work for them still. Bearing assemblies, motors, motor mounts, couplers. Great old pumps. they are 1725 rpm.0
-
My guess is could be the 1-1/2" also which is the hv on chart. I run into a lot of the hv and the 2" 1/6hp.
0 -
Thanks, everyone. I'll let you know how it turns out.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
That’s a PR.Retired and loving it.0
-
all right Dan, without a good look at the volute and of course the impeller, what was the clue to say PR not HV?
inquiring minds want to know?0 -
-
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements