adding makeup water break tank to closed system
capman
Member Posts: 2
Does anyone have any recommendations or feed back on keeping the old PRV Or removing it with fill tank system. My installer removed the old prv and says the new feed tank has an adjustable prv with a bypass on it with pressure guage so no need to keep the old prv from the system in operation. Its only a single system one pressure commerical hotwater heating loop. 2 story building.
0
Comments
-
per code they wanted air break and city would not allow a air gap back flow preventer they wanted a break tank fill system installed.0
-
They wouldn't allow a reduced pressure zone backflow preventer? How very odd. Presumably this thing has a self contained booster -- or you've piped one -- to fill from the tank. How is that booster controlled?
And what controls the level of water in the break tank (besides the overflow, of course!). In any event, I see no purpose in either a pressure reducing valve (PRV) on either the feed from the tank to the system -- the feed pump should operate only when the system actually needs water, and then the pressure feeding is irrelevant -- or on the feed to the break tankBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I'm thinking they took a larger expansion tank, pumped the bladder up to near city water pressure, then filled and pressurized it with a hose. The new prv would set the pressure in the system.
Pictures would help.0 -
If that's what is meant, it is NOT a break tank. Or at least I would never have approved it as such. No way.mattmia2 said:I'm thinking they took a larger expansion tank, pumped the bladder up to near city water pressure, then filled and pressurized it with a hose. The new prv would set the pressure in the system.
Pictures would help.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Of the feed tanks I've seen, the pump in controlled by a system pressure switch. The tank simply has a low level float which will not allow the pump to run and closes alarm contacts, which turn on a light, dialer, and/or lock out the burner.
Tank would be filled manually generally a glycol system.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements