Rotting heat exchangers
Riles_5
Member Posts: 13
We have a customer who i sold a boiler too, they have gone through 2 heat exchangers in probably 5 years this last one lasted only 3 years. They have tested the water in the boiler telling me it is fine, there is antifreeze in the loop. To go through 2 heat exchangers, stainless steel is unheard of. Any help would be helpful.
They tested the anti freeze, with test strips.
They say that the boiler was set up properly, and cleaned annually
They tested the anti freeze, with test strips.
They say that the boiler was set up properly, and cleaned annually
0
Comments
-
What is the rest of the system like? only the boiler is being affected?
Do a full water test by titration, PH, dissolved mineral.
Could be over pumped and causing velocity erosion.
Has anyone ever seen electrolysis be an issue with stainless?0 -
They say the boiler was set up properly.
Hmmmmm.
Must be a lousy product then.😀
No, seriously, best show pics here for these guys, and also show entire room and the combustion printout and how long it was at those combustion numbers. (Steady state combustion)0 -
Do you know what side rotted out, water or flame?0
-
I include pic on Monday when i get to my work emails.
what i do know is that i asked for a water sample and the sample had antifreeze in it, i used cryo tek test strips to check it. it came back bright yellow on the strip for PH that said unsatisfactory i though, being told different from my outside sales person.
The pic i have of the heat exchanger my first thought was improper setup, i have been cleaning and setting up boilers for some time before taking a sit down job. but with out being onsite to see it first had its just my assumption.1 -
-
-
Did a water test 7.5 pH levels everything else looked normal.0
-
LP gas? Looks it from the Pix...May be time to switch boilers.0
-
-
I would venture to guess the rest of the system is copper or has copper in it. I think it would be hard to have water chemistry that would eat the boiler and not the copper or iron for that matter.
I would agree that it is likely the combustion side.
Or incorrect water flow, too much or too little?0 -
ch4man. lol..
That's not blunt thats the first thing i said to them when i saw it. not cleaned and not service, or not set up properly. Told it was cleaned last year. worst of all its NAT gas. or he never did a combustion test on it.
But that's my opinion.....0 -
That's easily solved by having them show you the results of the combustion analysis for that boiler, I would think if they were actually doing it they would be keeping the records. Would be foolish not to for this exact reason.Riles_5 said:
But that's my opinion.....
Working for an OEM manufacturer I know I would require that documentation before approving any warranty. Not that we do boilers, but I have required specific documentation prior to any warranty approvals on our products.
0 -
Ah... if that's the fire side in the picture -- seems like it -- where is the boiler located in relation to any other chemical storage? Particularly anything with Chlorine in it in any form? And what is the general air quality of the intake air? We sometimes tend to forget that combustion creates moisture, and if that reacts with anything … interesting... in the air, it can have very bad effects very quickly.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
water tube french heat exchanger I'm pretty sure. Combustion by products. Rotted from combustion side. Not been maintained would be my guess. We have had to clean those every year with maybe 10%-15% of the amount of coffee grounds as that one has annually. When the grounds build up the acidic condensate saturates the grounds and the crystals attack the stainless steel is what we have seen and deduced. Not too scientific of a deduction but its our assessment. We have found crystals attached to stainless and when you clean them off we have found pin holes at the attachment point. Don't find many lasting more than 8-10 yrs or less.2
-
How close is the intake and exhaust
Were they piped close together0 -
Even with good combustion #s after we have set these up after servicing they still build up every year. As I stated above not near as bad but 2 or 3 yrs of ignoring, especially I have found on potable hot water with these types of heat xrs. Just my opinion from experience. Btw, we don't install these just repair and maintain periodically.0
-
I dont think you can tell from that pic.
Yes it's very dirty with lotsa coffee grounds, but it looks like the rusty boiler water has been intruding for quite some time near the burner.
I agree with @Jamie Hall where is the combustion air coming from? Any swimming pools etc near by?
By the looks of this HX it's a 750,000 or larger input boiler in a large commercial building.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Chlorides?0
-
Not sure about chlorides. I did find out there was suppose to be some boiler re-piping, from the last heat exchanger replacement,That may not have been done. I just found out. thanks for all the input.
How do you close a discussion on here?0 -
Don't close it yet. Come back when you find the culprit.0
-
There are many grades of SS
Is this job on LP gas?
Are you pulling room air for combustion?
If pulling outside air for combustion do you have cross contamination?
Is this a combi boiler with internal pump?
If the primary pump is outside the boiler do you have the correct pump that the manufacturer recommends? I would say if you have a pump that is not moving the water fast enough the heat exchanger is getting to hot pulling impurities out of the exhaust flue gas and that crap there most likely is acidic sitting their eating away at the SS heat exchanger?
Was this boiler set up with testing equipment to the manufacturer specs?
Oh so many questions.
Is this boiler piped primary / secondary?
What did the manufacturer of this boiler say about your problem?
Please let me know what you find out.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements