Triangle tube noise on start up
CBRob
Member Posts: 283
The new prestige solo that I have set up for snow melt makes a bunch of banging and thumping noise when it fires up.
Yesterday I kicked it on manually just to check Delta temp and it actually banged a few times then shut it self down.
Return water temp was about 50. Running 50/50 glycol.
Should I be concerned
Yesterday I kicked it on manually just to check Delta temp and it actually banged a few times then shut it self down.
Return water temp was about 50. Running 50/50 glycol.
Should I be concerned
0
Comments
-
Not sure, but I would definately recommend tightening the brass nut connecting the supply outlet to the HX..
I’ve had almost everyone from the factory loose to the touch0 -
Cool. I'll check it out.0
-
-
He absolutely should and you should get a picture of the readings. You get an excellent warranty extension if you do.https://www.triangletube.com/support/warranties"If you can't explain it simply, you don't understand it well enough"
Albert Einstein3 -
-
Will also need static gas pressure and operating high fire gas pressure readings, just as if not more important than the combustion report. You can't set up the combustion without proper gas pressures operating and standing.
D0 -
> @DZoro said:
> Will also need static gas pressure and operating high fire gas pressure readings, just as if not more important than the combustion report. You can't set up the combustion without proper gas pressures operating and standing.
> D
Dz,
Is that something you check on every new install or just when there is something strange going on?0 -
Combustion and gas pressure tests are a absolute must on every job. No 2 jobs are alike, no two boilers are alike they look similar but are very different in operational settings.
Sometimes you may not have to touch a thing, but more often than not I find that tuning is needed, high fire, low fire, and gas pressures.
One cannot set one without the other. Always start with gas pressure standing, then gas pressure high fire, after that is all correct then you can perform the high fire combustion testing, set accordingly and only after that is all proper go to the low fire setting of combustion analysis.
D1 -
Banging could be a flow problem.
Why 50% glycol, way too much unless you are at the North Pole.0 -
maybe not the north pole, but we will get occasional 30 below.
My boiler guy got stung years ago with some freeze damage and he's probably a little paranoid now.
The exhaust flue is a pretty short run with proper pitch. I'm sure no obstructions. the noise is similar to knocking on a door.
When I kick on the system using the tekmar control I put it right into full blast. Could that have an impact? would a boiler that's using its internal settings start low and ramp up?
My research tells me that this noise is often the water boiling in the heat exchanger.. But that seems so unlikely.
the circ pump works and the temps when I start it off are always pretty cool, like 40s or 50s
there is also a low loss header, so its not getting any super cool slab temp water right off the bat either.
I'll go fire it up again today and record it.
0 -
@Steve_WheelsSteve_Wheels said:Banging could be a flow problem.
Why 50% glycol, way too much unless you are at the North Pole.
It is a snowmelt system in zone 8 ~9,500' elevation
The north pole may be warmer"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Did you put the air vent on the top of the boiler?
May also have to flush air out with the pressure relief valve.
D0 -
yep, got the air vent installed.
here is the setup.
0 -
is there a fast fill? And the vent on top of the boiler? hard to tell with that picture.. Banging tells me it's a flow issue. Generally set up is howling... what is the pressure on the system? Also gas line doesnt have a sediment trap or shut off If I'm picturing it right.. I would ask the manufacturer what the maximum amount of antifreeze allowed is...0
-
Is it on the top of the boiler, by the relief? Hard to see behind the relief valve0
-
Is the air vent hidden behind the prv?
Is it open? Air trapped in the upper portion of the HX could make the noise you describe.
Triangle Tube is OK with 50% glycol."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
@SeanBeans
Hygroscopic, go figure, kind of like inventing a new wheel, why would you put a cap on there if you aren't supposed to use it
Thanks for the heads up.
@CBRob , I would make sure the valve is working and there is no air. Since the PRV is brand new, you could give it a quick burp."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Here is a video I just shot of the boiler making its noise.
I've drained and filled other tri tube boilers and never had this noise.
https://youtu.be/T21P4wI28Q80 -
-
Thanks DZ.
I'll let you know how it goes0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements