CO Scare
Dan Foley
Member Posts: 1,260
I got a call this morning. The CO monitor had alarmed last night so my client shut down the boiler. The high reading was 100 PPM.
I sent Brian out today to check out the Buderus cast iron atmospheric draft boiler we had installed about 12 years ago.
The chimney was drafting, burners were clean and the sections were clear - no soot.
Three of the chambers were reading within specs, less than 100 PPM CO. The fourth chamber spiked over 2,000 PPM CO.
After re-checking everything, Brian finally found the cause. He took apart the in-shot birners and found this dead snake inside. It was fouling up the fuel-air mixture creating the high CO. This could have ended up bad.
I sent Brian out today to check out the Buderus cast iron atmospheric draft boiler we had installed about 12 years ago.
The chimney was drafting, burners were clean and the sections were clear - no soot.
Three of the chambers were reading within specs, less than 100 PPM CO. The fourth chamber spiked over 2,000 PPM CO.
After re-checking everything, Brian finally found the cause. He took apart the in-shot birners and found this dead snake inside. It was fouling up the fuel-air mixture creating the high CO. This could have ended up bad.
-1
Comments
-
At least it didn't bite him............
Nice catch!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Wow! Thank god for CO meter. I started carrying a personal CO meter with me years ago and I was amazed at how many boiler rooms had CO in them. Worst one I walked in on was 4,000 ppm. 2 million btu atmospheric American Standard boiler. Customer said the boiler room was too cold and cinder-blocked in the combustion air openings.Never stop learning.2
-
-
Mike and Steve,
Which personal CO meter are you using?0 -
https://images-na.ssl-images-amazon.com/images/I/3118ZVK0ATL.jpg
https://www.amazon.com/Tough-Waterproof-USA-Made-Intrinsically/dp/B00DRJ1KQO/ref=asc_df_B00DRJ1KQO/?tag=hyprod-20&linkCode=df0&hvadid=312114659020&hvpos=1o1&hvnetw=g&hvrand=16041360409347625351&hvpone=&hvptwo=&hvqmt=&hvdev=t&hvdvcmdl=&hvlocint=&hvlocphy=1024699&hvtargid=pla-569855003664&psc=1There was an error rendering this rich post.
3 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements