Type IV Boiler vent
Options
newinnj
Member Posts: 64
Hi,
I have a Navien NB-150 condensing boiler. The boiler vent collars have a tiny gap between the collar and the boiler. First should this be sealed? I am thinking yes. If so, any recommended material to seal the gap. Thanks in advance.
I have a Navien NB-150 condensing boiler. The boiler vent collars have a tiny gap between the collar and the boiler. First should this be sealed? I am thinking yes. If so, any recommended material to seal the gap. Thanks in advance.
0
Comments
-
Open it up and look inside. Are there solid pipes passing thru the collars? The gas may be only on the flange and not the actual pipe itself.0
-
You are correct and thanks! Pipes inside the boiler goes up and past the collars into the external pipes.0