Pvc venting

CBRob
CBRob Member Posts: 283
I've heard that foam core pvc is not approved for venting condensing boiler.
Is that true for all boilers, and does cellular core mean foam core?

Comments

  • Zman
    Zman Member Posts: 7,610
    Yes, cellular core is the same as foam core. It is OK for combustion air piping. I don't know of a boiler manufacture that allows cellular core for venting.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    Jolly Bodgerdelta Tkcopp
  • ChrisJ
    ChrisJ Member Posts: 16,231
    Separate subject but, I didn't know hose clamps worked on PVC?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • JUGHNE
    JUGHNE Member Posts: 11,254
    I wonder if there is a rubber type gasket missing from that connection?
  • DZoro
    DZoro Member Posts: 1,048
    The gasket is just below the band. The band is just holding the pipe from coming out.
    Others are correct no cell core on exhaust, personally not even on intake. Too easy to get mixed up during installations.
    D
    ChrisJdelta TZman
  • CBRob
    CBRob Member Posts: 283
    Uh oh...
    This is the exhaust side.

    I've got a feeling it's the same pipe all the way to the roof.
    And probably the same on 10 of these houses.

    How big of a deal is it?
    I hate to be an alarmist with informing owners.
  • ChrisJ
    ChrisJ Member Posts: 16,231
    CBRob said:

    Uh oh...

    This is the exhaust side.



    I've got a feeling it's the same pipe all the way to the roof.

    And probably the same on 10 of these houses.



    How big of a deal is it?

    I hate to be an alarmist with informing owners.

    If it's against code and not approved by the manufacturer I don't know.

    I guess it depends on if something goes wrong or not.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Steamhead
    Steamhead Member Posts: 17,317
    I would alert the owners and make whoever put it in eat the replacement cost.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    delta T
  • JUGHNE
    JUGHNE Member Posts: 11,254
    My son's condo had used cell core for his condensing furnace.
    A lot of horizontal pipe. Stains in the ceiling. Combination of bad glue joints, sagging pipe and lack of support. Enough sag that you could hear water bubbling and suddenly a blast of water coming out.
    Problems were not necessarily because of cell/foam core pipe but it's use was another item indicative of a cut corners and get it done job.
    I told him to talk to the contractor about it.
    They redid several 5 unit condos at their expense and also sheetrock repair included. (I was surprised)
    The HVAC sub had sub-let the original job out.
  • ChrisJ
    ChrisJ Member Posts: 16,231
    JUGHNE said:

    My son's condo had used cell core for his condensing furnace.
    A lot of horizontal pipe. Stains in the ceiling. Combination of bad glue joints, sagging pipe and lack of support. Enough sag that you could hear water bubbling and suddenly a blast of water coming out.
    Problems were not necessarily because of cell/foam core pipe but it's use was another item indicative of a cut corners and get it done job.
    I told him to talk to the contractor about it.
    They redid several 5 unit condos at their expense and also sheetrock repair included. (I was surprised)
    The HVAC sub had sub-let the original job out.

    What is foam core actually intended for?
    Outdoor drainage? Is it actually used indoors for DWV?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • roelandp
    roelandp Member Posts: 6
    are there orange stickers saying 636 on the fittings
  • roelandp
    roelandp Member Posts: 6
    this is an approved venting system in canada if it has stickers and pipe that says 636 were do you live
  • JUGHNE
    JUGHNE Member Posts: 11,254
    The big clue on the labeling I noticed in the OP earlier post states not for pressure. DWV only.
    (Regular 3" sch 40 dwv is rated for 260PSI at 73 degrees F.
    .........even that's scary isn't it. )
    Foamcore is light weight. PVC shell outside and inside. The wall thickness is made up with high density foam sandwiched between the shells. Just picking it up the weight will tell you.

    Check some out at the big box, just compare weight and price.
    Not a lot of savings unless you are doing a lot of pipe IMO.
  • CBRob
    CBRob Member Posts: 283
    These houses are passed the contractor warranty. For the state of Colorado. I think it's 6 years here. So the homeowners would be on their own.
  • GroundUp
    GroundUp Member Posts: 2,069
    Some places cellular core is acceptable. One of my competitors here uses it for everything and always has, passes inspection every time. Personally I use solid for everything, so it doesn't get mixed up, and it's an extra dollar per job so I have no idea why anybody would try foam core in the first place
    delta T
  • ChrisJ
    ChrisJ Member Posts: 16,231
    > @JUGHNE said:
    > The big clue on the labeling I noticed in the OP earlier post states not for pressure. DWV only.
    > (Regular 3" sch 40 dwv is rated for 260PSI at 73 degrees F.
    > .........even that's scary isn't it. )
    > Foamcore is light weight. PVC shell outside and inside. The wall thickness is made up with high density foam sandwiched between the shells. Just picking it up the weight will tell you.
    >
    > Check some out at the big box, just compare weight and price.
    > Not a lot of savings unless you are doing a lot of pipe IMO.

    No, that's not scary.

    It's rated different pressures at different temperatures just like any pipe.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • JUGHNE
    JUGHNE Member Posts: 11,254
    Yes, true, but it is still PVC.
    The very few times I have had to deal with any pressure above 50 PSI for PVC, Sch 80 was used. You can even thread that.

    But being old school I don't even trust CSST either.
    I know.....old guys.
    However if I were doing cast iron DWV when PVC came along I most likely would have embraced that pretty fast.
    And if I were 40 years younger I would even get PEX tools.
    Still only copper or someone else does it.
  • Jolly Bodger
    Jolly Bodger Member Posts: 209
    Cellcore is only designed for Drain Waste Vent. And the vent they mean is plumbing vent not combustion vent. Cellcore has very low heat tolerance and will breakdown/sag. If you are installing a Boiler or water heater, the approved venting is dependent on what temperature the appliance is going to run at. That directly affect the flue gas temperature.

    Two things make this acceptable or not. The AHJ (authority having jurisdiction, local building department) and the UL listing. New construction so the AHJ signed off on it. This might mean it meats the local code or it might mean the inspector did not catch it.

    But if Cellcore pipe is not an approved venting material by the manufacturer and approved for the application (temp). Then the installation Voids the UL listing. An insurance company might have a problem with that.
  • Polaris water heaters still show that PVC is approved for vent and air intake pipe.