Why does my boiler have bad surging at start up, but as it goes the surging in minimal
Itmejvt
Member Posts: 4
At start up it is horrible, sometimes triggering the LWO, but as the cycle continues it bobs minimally. What are your thoughts, thank you
0
Comments
-
Is this a new installation? Even if it’s not was it skimmed when it was installed?0
-
1 year old, it’s was skimmed last year0
-
I would suspect oil on the water or dirty water, or water with too high a ph level (too many additives) or too high a water level, or an overfired boiler or a combination.
I would guess that at first the boiler is throwing water into the main(s) and after it does that a bit the water level goes down and things settle down.
Check those items and worst cast you can rule them out.
Also post pictures that are such that each one shows the boiler area from floor to ceiling, and take shots from several angles. The near boiler piping may be involved.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements