I have a bathroom in my house were the previous owner took out the radiator and now its freezing. The supply pipe is still under the bathroom capped off. I have a lot of 1/2" copper pipe and I was brainstorming how I could use it on my one pipe system. Since 1/2" is rather small I thought that steam and water cannot pass each other, at least not without a lot of water hammer. So in my diagram attached I am proposing a 2 pipe connection were steam comes in and since the radiator is pitched the water will return through the other side. In the return side there will also be a bend in the pipe acting as a water trap. So steam won't try to go through the return pipe. Let me know what you think and if it might work.

Comments

  • ethicalpaul
    ethicalpaul Member Posts: 6,663
    Question: why not just restore the original size feed to a one-pipe radiator?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • EzzyT
    EzzyT Member Posts: 1,344
    1/2” piping is to small and copper piping and fittings will eventually leak due to expansion and contraction rate.
    Do you know what the square footage of steam that the radiator you have is rated for? Based on the square footage output of the radiator then you determine what size riser pipe you’ll need with a properly sized valve.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • jewett44
    jewett44 Member Posts: 3
    > @ethicalpaul

    I could do that and that would be what I would do if this wasnt possible. I was just brainstorming alternative methods. More or less because I wanted to know if it was possible.
  • jewett44
    jewett44 Member Posts: 3
    @EzzyT
    I dont actually have the radiator yet. It is a small bathroom so I'm looking for something short and skinny so it fits tight to the wall. I was just theorizing if this would work. Even if it was 1/2 galvanized steel you think the pipe is too small?
  • EzzyT
    EzzyT Member Posts: 1,344
    Yes 1/2” piping is to small even if it’s copper or steel. You don’t want to use galvanized piping and fitting you’ll want to use steel pipe mailable or cast fittings.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • acwagner
    acwagner Member Posts: 512
    Be careful on selecting your radiator. Try to find an old one that was meant for steam.
    Burnham IN5PVNI Boiler, Single Pipe with 290 EDR
    18 Ounce per Square Inch Gauge
    Time Delay Relay in Series with Thermostat
    Operating Pressure 0.3-0.5 Ounce per Square Inch

  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    I've been looking at the CastRads radiators advertised on this site. They have a wide variety of sizes, styles and finishes, and can be set up for steam or hydronic systems.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
    jewett44
  • acwagner
    acwagner Member Posts: 512
    CastRads looks pretty cool.

    I recently used Ecorad to get some refurbished radiators that matched the rest of the radiators in my house for some remodeling we did.
    Burnham IN5PVNI Boiler, Single Pipe with 290 EDR
    18 Ounce per Square Inch Gauge
    Time Delay Relay in Series with Thermostat
    Operating Pressure 0.3-0.5 Ounce per Square Inch