Help with speed skimming on Slant/Fin
tomsloancamp
Member Posts: 88
I was wondering how to go about speed skimming a Slant/Fin Galaxy boiler. Unfortunately, Slant/Fin doesn’t provide any manual or publication about skimming. I’m including a photo for assistances because I’m not sure where to skim from?
0
Comments
-
-
Ok, I understand what you mean. What would I need to skim. I’m assuming I need some piping and a shutoff valve.0
-
Just slowly add water to a hot boiler, but not steaming, and allow the water to come out the skim tapping. The Slant Fin skimming is probably the best design in the industry since they have an extra large end section with a wide dam built in to allow very quick and very efficient skimming of the boiler. They also produce exceptionally dry steam with thier unusual internal passage design... again I think it is the only one in the industry set up that way. I would use thier equipment much more often, but the reps in Chicago are very poor. For the Galaxy, speed skimming is real.To learn more about this professional, click here to visit their ad in Find A Contractor.1
-
The skim port is usually just about at the water line. As @The Steam Whisperer Says. ( Slowly )........ fill the boiler to about halfpipe or less allowing the the flow of water to "skim" the debris from the water surface.0
-
There is piping coming out around the water level line the has a cap on it. Can I just remove the cap or do I need to by some pipe and add a shutoff valve. Would I put the cap back on after skimming is complete?0
-
I purchased a 3/4 in. galvanized coupling, 3/4 in. X 8in. Gal steel pipe nipple, and a 3/4 brass ball valve. Will this do for a skim valve assembly? Also the manufacturer states to drain 1-2 inches below skimmer tapping. Can I use the sight glass as a gauge?0
-
Sounds about right.tomsloancamp said:I purchased a 3/4 in. galvanized coupling, 3/4 in. X 8in. Gal steel pipe nipple, and a 3/4 brass ball valve. Will this do for a skim valve assembly? Also the manufacturer states to drain 1-2 inches below skimmer tapping. Can I use the sight glass as a gauge?
You can use the sight glass as a line of sight but that depends on your boilers tappings.
Add water to the hot boiler at about half pipe or less. Slowly.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements