Boiler temp vs high temp setting
JohnKV
Member Posts: 12
in Oil Heating
I noticed my brand new Honeywell L8148A 1017 can be set for 190 degrees but boiler only reaches maybe 175. It was suggested the well wasn’t packed with grease (which is true) and may be causing the difference. My research suggests this grease will harden eventually so I’d rather avoid it. Question is, would it be safe to crank the high limit to say, 210 to make the boiler reach 190?
0
Comments
-
Why so hot?
95% of the time 175* is more than enough water temp. for many designed systems. Are you having a issue with the system not reaching a constant set point.
Are you sure that the boiler thermometer is accurate?
D0 -
Heats wonderfully. I I don’t believe the aquastat is accurate. My mercury thermometer on my upper boiler piping matches my tridicator on my boiler. Just falling 20 degrees short of my aquastat high temp setting when she shuts down0
-
I’m assuming a longer burn cycle would be more efficient, if there’s still a call for heat, shouldn’t it hit the high temp limit then shutdown?0
-
Does the boiler shut down at 175? Or is it that it just sits there running and doesn't go any higher? If it's the latter, are you sure that that simply isn't where it will go when the heat input at the boiler is equal to the heat output at the radiation?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Boiler shuts off at 175 like it hit its high limit, still a call for heat.0
-
-
It’s in the 30’s and 20’s here in Wisconsin at night lately, but it heats very well and barely runs it seems. If I set the high limit to 160, it runs for a few minutes every 10 or 15 minutes. I believe that’s called short cycling?0
-
-
Turning it up will make it worse. What size is the boiler and how large of a home do you have?
During this transitional season most standard boilers will be short cycling. When your design low temperature approaches anywhere from 0* to-16* will be where your boiler should run non stop, and maintain a constant set point. If it was sized perfectly, and nothing is perfect in this world
D1 -
I think it’s about 79,000 BTU, house is 1,655 square feet. 6 cast iron rads downstairs and one for the entire upstairs which is an almost 800 square foot master bedroom. It heats that whole upstairs surprisingly well with one rad. So far anyway, it’s not super cold yet either.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements