Smart thermostat with hydronic heating, 2 zones
wiseplant
Member Posts: 1
Hi All, new homeowner here learning the ropes of hydronic heating. I am attempting to install an ecobee 4 smart thermostat with my 2-zone system controlled by Taco zone valves and am trying to deciper this wiring diagram. How do the zone valves on this image correlate to the three terminals on the Taco zone valve?
https://support.ecobee.com/hc/en-us/articles/234939667-ecobee3-lite-with-4-wire-hot-water-zone-valves
Thanks in advance
https://support.ecobee.com/hc/en-us/articles/234939667-ecobee3-lite-with-4-wire-hot-water-zone-valves
Thanks in advance
0
Comments
-
3 terminals. You probably have the Taco 550 series zone valves. Here's a cut sheet. The Common wire in the Taco diagram that goes from the transformer to the #2 terminals on the zone vales also connects to the C terminals on the thermostats.0
-
A word of caution: hydronic systems have much slower response than forced air. Using a setback or smart thermostat can be very counterproductive to the way they operate and may actually save no energy while sacrificing comfort.
The best thing you can do is set it (the stat) and forget it.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements