Do you need an aquastat when adding scavenger loop to steam boiler

FTWIII
Member Posts: 14
I want to add approx 20' of baseboard off a steam boiler. I want to be able to control it independentaly from the steam. I know about the flow controls, by-pass, thermometer and bronze circulator. But don't I need an aquastat to fire the boiler if boiler isn't running for the steam?
Is there any other circ, other than bronze B&G 100?
Is there any other circ, other than bronze B&G 100?
0
Comments
-
Yes, you would need an aqua stat to fire the boiler if it isn't running for steam.
All you could want to know is here: https://heatinghelp.com/systems-help-center/how-to-run-a-hot-water-zone-off-a-steam-boiler/NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Thank you. I was confused since all diagrams I've seen didn't show an aquastat0